16 comments
Rate Comments: Nested
Participant

Join Date: May 2009
Posts: 4

Do we need isolation between PLC and Field instrument

05/24/2009 1:50 PM

Hi friends Iam new to this site and found very interesting. I hv got a question. We are under industrial construction ,in my control loop i got both loop power supply and self power of a field instrument( for eg : Mag flow self power with 110 VAC and loop power source 24 VDC) two source power in same line will it damage the instrument /Modules. Do we need to isolate any one. If yes,how external isolator need to be provided or all receiver hv inbuilt isolator and we need to do connection changes. Can explain plz. regards Pravin

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#1

Re: Do we need isolation between PLC and Field instrument

05/24/2009 5:59 PM

Hi, Pravin,

Sounds like you've got a reasonable question in there somewhere, but I can't quite find it. Can you please explain a bit more clearly? Posting a sketch of your system (just one input point) showing the power supply and signal routes would help.

This thread from Sparkstation (bless him wherever he is) explains how to post images.

John

__________________
"Love justice, you who rule the world" - Dante Alighieri
Register to Reply
Active Contributor

Join Date: Nov 2008
Posts: 13
#2

Re: Do we need isolation between PLC and Field instrument

05/25/2009 12:52 AM

hi - correct me if I am wrong

to my knowledge you need to have isolator because when you see in the case of earthing as there are two different types of supply in the same loop there will be difference in power flow in this case you need to have isolation such that this difference will not effect the earthing system....

regards

foreveryone

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#15
In reply to #2

Re: Do we need isolation between PLC and Field instrument

05/26/2009 4:13 AM

The output signal might be galvanically isolated from the power leads, in which case, no problem. Check the manufacturer's information supplied with the equipment.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#3

Re: Do we need isolation between PLC and Field instrument

05/25/2009 2:23 AM

Hi there,

You will use an isolator (galvanic) if the instrument is in a hazardous (zoned area).

Another point worth making - do not run your power supply and your instrument signal in the same cable, or in the same rack - you will only open yourself up to interference.

It sounds as if your instrument is not loop powered, in other words the instrument is supplying the 24VDC for the loop in the signal cable. If this is the case, you need to check your PLC/DCS analogue input card. Some of them allow for this type of connection (refered to as a 4-wire loop). If this is the case, you do not need an isolator.

If the input card does not allow for this, then you will need a signal isolator.

You can look at www.weidmuller.com for more information on a signal isolator.

Regards,

Craig

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#13
In reply to #3

Re: Do we need isolation between PLC and Field instrument

05/26/2009 4:10 AM

<...You will use an isolator (galvanic) if the instrument is in a hazardous (zoned area)....>

Eh? Not if the method employed to prevent incendive sparks from igniting the atmosphere complies with European standards.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: May 2009
Posts: 15
#4

Re: Do we need isolation between PLC and Field instrument

05/25/2009 3:11 AM

I would recommend it and it maybe as simple as using ceramic capacitors and ferrite beads as inductors in a "T" network. It really depends on the frequency of the conversion from AC to DC and the relative load of the instrumentation with respect the control loop.

Times ten rule applies to this one!

Register to Reply
Participant

Join Date: May 2009
Posts: 4
#5

Re: Do we need isolation between PLC and Field instrument

05/25/2009 4:44 AM

Hi Gents,

Thank you all for your replies.My concern is, for instant let us consider a mag flow meter which has 110/220 VAC supply what will be the voltage in that 4-20mA output wire to PLC.

It will take time for me to check practically in field , Please let me know .

regards

Pravin

Register to Reply
Active Contributor

Join Date: May 2009
Posts: 15
#11
In reply to #5

Re: Do we need isolation between PLC and Field instrument

05/25/2009 1:23 PM

No, 4-20mA is Loop current not voltage and the low (Zero) signal level being 4 mA is part of the standard for noise immunity since noise current at 0 mA would be much more of a factor than noise current at 4 mA. The second very important part is that it is "Loop Current" and running both wires of the loop through a two hole ferrite bead should be all you need.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12
In reply to #5

Re: Do we need isolation between PLC and Field instrument

05/26/2009 4:08 AM

<...what will be the voltage in that 4-20mA output wire to PLC...>

Whatever it needs to be to overcome loop resistance plus the input resistance and supply 4-20mA. For a current loop, the voltage is largely irrelevant.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#6

Re: Do we need isolation between PLC and Field instrument

05/25/2009 5:16 AM

Hi there,

Chances are that you will have between 16 - 24VDC in the 4 - 20mA line.

Regards,

Craig

Register to Reply
Participant

Join Date: May 2009
Posts: 4
#7
In reply to #6

Re: Do we need isolation between PLC and Field instrument

05/25/2009 5:46 AM

Hi craig

Thanks for your reply.Oops!! then if the plc also giving power supply(24 VDC) to that loop either one should be isolated otherwise its going to damage the instrument/module rite.

regards

Pravin

Register to Reply
Commentator

Join Date: Jun 2008
Location: Brick, NJ
Posts: 71
Good Answers: 8
#8
In reply to #7

Re: Do we need isolation between PLC and Field instrument

05/25/2009 5:56 AM

If the instrument is supplying power to the loop is is normally the case with mag meters, the the PLC must not be configured to also source 24VDC. The PLC card needs to be set to sink and not source. You also need 2 conduits to the mag. One to provide power to the mag and one for the 4-20mA loop. The only isolation I typically use on the 4-20 loop if I am not installing it in a hazardous area is a fuse on the + line before the PLC input.

__________________
Do this. Don't do that. Can't you redesign?
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#16
In reply to #7

Re: Do we need isolation between PLC and Field instrument

05/26/2009 4:14 AM

Using a separate power supply, rather than the PLC power supply, is highly recommended.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#9

Re: Do we need isolation between PLC and Field instrument

05/25/2009 6:09 AM

Hi there,

If the PLC analogue input card is giving power to the loop and the instrument is giving power to the loop - you need a signal isolator.

You should not damage anything if you connect it up without a signal isolator - the loop will just not work. Remember it is the current that destroys the channel, you are limited to 22mA either way.

I have found (with Siemens equipment) that if I connect more than one 4 wire loop to a card configured for 2 wires that it pulls the other channels down (the voltage).

Another thing to check with 4 wire loops is the grounding. If done incorrectly you will destroy your input card as the current will pass through the channel to ground. You will have to refer to your equipment specific manuals for this.

Regards,

Craig

Register to Reply
Participant

Join Date: May 2009
Posts: 4
#10
In reply to #9

Re: Do we need isolation between PLC and Field instrument

05/25/2009 7:27 AM

Hi gents

From my past experience working with Honeywell EPKS - DCS, in their FTA card they hv a option for changing the connection in this type of suitation.But in my current project we using national instrument PAC - I/O modules, anyone worked on NI-PAC ,do they hv these options. I read ther manuals they hv given some circuit connection i want to be clear whether its for the same scenario otherwise i need to provide external isolator.

regards

Pravin

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#14

Re: Do we need isolation between PLC and Field instrument

05/26/2009 4:12 AM

<...two source power in same line...>

....is not recommended. It is always better to put the power supply in one cable and put the signal return in another. For that reason, most magflos have 2 cable entries.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply