How to avoid dust related problems on electrical equipment? if we are unable to control the dust.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#1

Re: Dust related problems

05/25/2009 4:47 AM

What kind of electrical equipment are you talking about. PLC?....Contactor?.....Timer?..... control panel?... and what kind of dust you are talking about.. Minor normal dust or heavy dust....? or heavy dust with metallic particle

Please elaborate more.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Member

Join Date: Apr 2009
Posts: 5
#2

Re: Dust related problems

05/25/2009 6:49 AM

All electrical equipments.Like conveyor motor feeders,contactors,JB & PLC also.Dust means lime dust & other steel raw material dust.

Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: Dust related problems

05/25/2009 11:33 AM

Put your control components into well gasketed dust tight enclosures. That's why they make them. If you are in North America, that would be UL/NEMA/EEMAC type 12 or 4. If you are in any other country, that would be IEC type IP54 or better (for example, IP55, IP65 etc.)

As to motors, you need to use TENV (Totally Enclosed Non Ventilated) or TEFC (Totally Enclosed Fan Cooled) motors. Again in IEC countries, that would be IP54 or higher.

If the dust still gets in through the gaskets, the next level of protection is to go with a "Purged Air" system. They use filtered instrument quality compressed air to pressurize the enclosures so that nothing gets in. These are typically used on Explosive Atmosphere locations, but can also be used for fne dust. They are very epensive however, and it is often less expensive to justmove the controls to a cleaner area.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#5
In reply to #2

Re: Dust related problems

05/26/2009 1:59 AM

Electrical Equipment for conveyor like motors feeder are design for dust proof with IEC standard of IP54 or IP56. It should not be a problem if the lime dust is on the motor, just use normal air to dust blow it once a weeks or twice a weeks. That is normal. These motor are design for it and you cannot cover the motor with enclosure, otherwise your motor will have no air for circulation and your motor will burnt.

There are some dust proof Junction boxes available in the market. These junction box have rubber seal at the door and when you close the junction box cover, the rubber seal will press against the box and no dust will able to enter. Of course you can use double junction box to protect the dust entering in to your JB.

If we has a PLC install at these dusty area, we always use double junction box for the protection from the dust and in these junction box, what we do is, to pressurize the junction box with a very small flow of nitrogen gas. You have to use nitrogen gas because these nitrogen gas is very dry and does not have any moisture in it.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Guru
Popular Science - Weaponology - New Member Netherlands - Member - New Member Fans of Old Computers - Commodore 64 - New Member

Join Date: Sep 2007
Location: Japan
Posts: 2703
Good Answers: 38
#4

Re: Dust related problems

05/25/2009 11:49 PM

If it is in an enclosed area fresh (filtered) air is key. you could also use air ionizers.

__________________
From the Movie "The Big Lebowski" Don't pee on the carpet man!
Register to Reply
Power-User

Join Date: Jul 2007
Location: Hyderabad, India
Posts: 212
Good Answers: 3
#6

Re: Dust related problems

05/26/2009 8:26 AM

Seal the cabinet with required degree of protection and install panel coolers for the health of electricals. There are a variety of Panel coolers available in the market.

__________________
B +ve
Register to Reply
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

capri (1); Epke (1); JRaef (1); LAVANaNB (1); Simon Wan (2)

Previous in Forum: Arc flash Category 0   Next in Forum: Tripping of conveyor,vibro feeder motors without reason

Advertisement