Anonymous Poster

Arc flash Category 0

05/25/2009 12:04 AM

At my facility, it is not uncommon for shop floor employees to flip disconnects (fuse switches) or circuit breakers inside a panel. What level of protection do I need for these folks?

I cannot find an answer. If I look in NFPA 70E 2009 it states "Cat. 0, Non melting clothes". Unfortunately for me, I have a unionized shop floor where there is no dress code so I cannot mandate clothing requirements. I also heard at an Arc Flash Conference that I cannot just give out FR clothing or FR smocks because they cannot be worn over melting clothes.

Bottom line, I'm just trying to figure out how to protection against Cat. 0 because if you read NFPA 70E then it states no FR clothing is required until over 1.2 cal/cm2 which is a second degree burn. I do not want to protect up to a second degree burn (OSHA recordable). I am at a loss on what to do to protect my workers. In addition to the PPE, is training required for these folks beyond LOTO?

Thank You, any help is appreciated.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Arc flash Category 0

05/25/2009 12:30 AM

Well without looking at the standard, my understanding of "Cat. 0, Non melting clothes" are clothes made of materials that don't melt (such as cotton) as apposed to clothing made of fibres that do melt (like man-made oil-based fibres and material).

It's a start.

Does NFPA have a glossary clearly defining what "Non melting clothes" means (most of the standards I deal with do)?

__________________
jack of all trades
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Arc flash Category 0

05/26/2009 3:29 AM

<...What level of protection do I need for these folks?...>

A lock on the panel, for a start, so that its interior is only available to authorised persons.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User

Join Date: Nov 2008
Location: US - TEXAS
Posts: 196
Good Answers: 18
#3

Re: Arc flash Category 0

05/26/2009 7:40 AM

NFPA 240.82(D) requires the breakers to be Switch Rated if they are used for that type of duty. No Cat 0 should be required if they are rated for switching.

If Union Members are switching circuit breakers on and off machinery and the circuit breaker and enclosure is not listed as a switch. They would have to be trained to energize and de-energize equipment in the proper manner not with the use of the overcurrent protection which should only be used by properly licensed and trained personnel. If they still insist on using the breakers, I would contact the union representatives in writing and notify them that there members are in direct violation of proper safety procedures and if they need to be instructed to work safely or be removed from the property.

If you have no other means to disconnect equipment other than the overcurrent protection device. Then you need to contact the engineer or supplier or some one of authority and ask them to produce evidence that the operation of such a device is proper and safe (in writing of course). Or ask them for proper instructions for a start-up and shut-down procedure, and train your personnel the proper operation.

Reply
Associate
United States - Member - Member Engineering Fields - Power Engineering - New Member

Join Date: Jun 2007
Location: Texas
Posts: 52
#4

Re: Arc flash Category 0

05/26/2009 9:01 AM

Your assumptions are mostly correct.

First union or non union, I can't imagine an industrial facility where the mandating appropriate work clothing is not acceptable. Especially PPE for a task with a defined set of hazards. Steel toed shoes, Eye protection, hearing protection, back support?, non-melting clothing?; its a very logical progression. The worst thing you get into, is that the union will want you to provide any "Specialty" PPE and they will probably have the support of OSHA regs.

The first thing you do is define the operation of said device(s) as a standard task with hazards. Then under OSHA you are required to train your folks to the "qualified" status. You'll add this standard task to the job definition of your plant operators and electricians. Then no other craft will be authorized to perform the task. Train your operators and electricians and then provide PPE as necessary.

It will cost you some $$$$, so just get ready.

Get a copy of NFPA-70e and the CFR's read them thoroughly, put in page tabs and highlight passages that apply. Then throw them down on the desk of the management/labor every time they give you static.

As a last resort, you could call your OSHA office and talk to them about requirements. But take care to keep the conversation anonymous unless your on good terms with the local inspector.

Reply
Power-User
Hobbies - CNC - New Member Canada - Member - Finaly got around to it.

Join Date: Feb 2008
Location: Canada
Posts: 499
Good Answers: 12
#5

Re: Arc flash Category 0

05/26/2009 4:38 PM

Here we are required to use a face shield, high voltage resistance gloves, that have to be certified and retested on regular schedule, and a proper apron. The good old fashion leather one is the best deal. That said, in 40 deg C. heat they are not very happy campers. They are more likely to die from heat stroke than from an arc flash.