Transformer Protection

05/26/2009 9:11 PM

Dear All,

Is there a standard or rule of thumb, what type of transformer protection should be provided based on the kVA ratings?

Regards.

__________________
"I know less than all, but more than many who know less"
Register to Reply
Pathfinder Tags: Transformer Protection
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#1

Re: Transformer Protection

05/26/2009 10:16 PM

NOPE. All Transformer have their standard type of protection provided by the transformer manufacture.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Transformer Protection

05/26/2009 10:21 PM

For 600 volt and below the primary over current device is 125% of the FLA. This can be changed under certain provisions. Your local code made dictate your choices.

Register to Reply
Anonymous Poster
#3

Re: Transformer Protection

05/27/2009 12:02 AM

Dear,

Please Go through IS 2026 if you are working for indian project otherwise go IEC60076 section 1 to 11 .

Regards,

Vikas

Register to Reply Score 1 for Good Answer
Associate

Join Date: Nov 2007
Location: Indonesia
Posts: 29
#4

Re: Transformer Protection

05/27/2009 3:06 AM

What I mean is the relay protection. For example, it's not common to provide differential protection for 1250 kVA transformer.

__________________
"I know less than all, but more than many who know less"
Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#5
In reply to #4

Re: Transformer Protection

05/27/2009 3:27 AM

Every country has it own electrical standard code to follows. Down here, small transformer like 11KV/433V from the lowest KVA till 8500KVA, we does not need to install the differential protection for transformer. We just install SPAJ and Earth Faults relay and these both relay is sufficient to protect your transformer.

Only our 35MVA transformer and the 120 MVA transformer, we do install the differential protection including the Overcurrent Protection and Earth faults Relay.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Associate

Join Date: Apr 2009
Location: DR Congo
Posts: 31
Good Answers: 2
#6

Re: Transformer Protection

05/28/2009 5:02 AM

Protection is always require for any equipment. But what all protections to be provided for specific equipments depends on many things like criticality of equipment, application of equipment, probability of re-occurring faults & of course cost involved in the protection.

There is a thumb rule for any protection system. Cost of protection the system should be less then 10% of the equipment to be protected. But normally as you go on bigger equipments this % ratio will come down & for smaller equipments % ratio will be more. Now because of numerical relays this ratio is again going on higher side but it has its own advantages so this is techo - commercial matter.

I have put numerical relays like &SJ61 for motors rating up to 55 kW, due to the criticality of the equipment. In this case %ratio is too high. But over all cost of electrical system & protection cost is again within 10%.

Register to Reply
Anonymous Poster
#7

Re: Transformer Protection

05/30/2009 6:57 AM

It is preferred that above 5000KVA you should have complete protection of transformer i.e Differential protection,Bucholze Protection.Pressure relaease device & High Winding temperature protection If your transformer is equipped with on load tap changer then its protection. Below this rating you can run transformer with basic protection i.e Over current protection either through switchgear or by providing blow out fuses this is a basic criteria looking to the cost of transformer its protection cost increses.

Anurag

Register to Reply
Associate

Join Date: Nov 2007
Location: Indonesia
Posts: 29
#8
In reply to #7

Re: Transformer Protection

05/30/2009 8:03 AM

Thank you. That's exactly what I need to know.

__________________
"I know less than all, but more than many who know less"
Register to Reply
Register to Reply 8 comments

"Almost" Good Answers: