Zig Zag Transformer

05/28/2009 4:09 PM

Hi All

I like to know about Zig zag Transformer, Is it just a method of connecting windings or is it a special type of winding. Please tell me about this transformer and its advantages, disadvantage and about its connections, please attach a connection diagram if anyone has.

Regards

JK

Register to Reply
Pathfinder Tags: Zig zag Transformer
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Zig Zag Transformer

05/28/2009 5:07 PM

Google "Zig zag Transformer"

Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#2

Re: Zig Zag Transformer

05/28/2009 10:46 PM

A zigzag transformer is a special purpose transformer. It has primary windings but no secondary winding.

As with other three phase transformers, the zigzag transformer contains six coils on three cores. The first coil on each core is connected contrariwise to the second coil on the next core. The second coils are then all tied together to form the neutral and the phases are connected to the primary coils. Each phase, therefore, couples with each other phase and the voltages cancel out. As such, there would be negligible current through the neutral pole and it can be tied to ground.

If one phase, or more, faults to earth, the voltage applied to each phase of the transformer is no longer in balance; fluxes in the windings no longer oppose. Zero sequence (earth fault) current exists between the transformer's neutral to the faulting phase. Hence, the purpose of a zigzag transformer is to provide a return path for earth faults on delta-connected systems. With negligible current in the neutral under normal conditions, engineers typically elect to under size the transformer; a short time rating is applied (i.e., the transformer can only carry full rated current for, say, 60 s).

An application example: Occasionally engineers use a combination of Y (wye or star), delta, and zigzag windings to achieve a vector phase shift. For example, an electrical network may have a transmission network of 110 kV/33 kV star/star transformers, with 33 kV/11 kV delta/star for the high voltage distribution network. If a transformation is required directly between the 110 kV/11 kV network the most obvious option is to use 110 kV/11 kV star/delta. The problem is that the 11 kV delta no longer has an earth reference point. Installing a zigzag transformer near the secondary side of the 110 kV/11 kV transformer provides the required earth reference point

You can find more information at http://en.wikipedia.org/wiki/Zigzag_transformer

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply Score 1 for Good Answer
Power-User

Join Date: May 2008
Location: San Jose, CA, USA
Posts: 121
Good Answers: 2
#3
In reply to #2

Re: Zig Zag Transformer

05/29/2009 12:59 PM

Simon,

I do not think the statement "It has primary windings but no secondary winding." is correct.

The purpose of any transformer is to change voltages. It has to have 2 (normally galvanic isolated) windings; in case of an autotransformer, one winding (part of it) is used by both the primary side (input) and the secondary side(output) (not galvanically separated).

This is not the case for a zig-zag connection transformer, who has 2 windings (primary/input and secondary/output). One winding (usually the primary side) can be connected in delta or Y/star, while the other winding (usually the secondary) is divided into 2 halves and are interconnected as described by you (and shown in the image).

But it definitely has 2 windings. The description given in Wikipedia is confusing (in my opinion) since it refers to the 2 halves (of the secondary winding) as primary and secondary.

__________________
Scientes et audaces fortuna juvat !
Register to Reply
Associate

Join Date: May 2009
Posts: 32
#5
In reply to #3

Re: Zig Zag Transformer

06/03/2009 12:47 PM

Sir thanks for your information, But I don't get a clear idea about this transformer can you please explain me this in a simple way with a simple winding connection digram or please tell me a site address or E-book address to know more about this transformer

Regards

JK

Register to Reply
Power-User

Join Date: May 2008
Location: San Jose, CA, USA
Posts: 121
Good Answers: 2
#6
In reply to #5

Re: Zig Zag Transformer

06/03/2009 2:39 PM

JK,

In the first picture in Simon's response you have a connection (star/Y). This is symbolically representing 3 cores with 3 coils around them (A,B,C). Each coil has an input end (at the junction connection) and an output end (at the output/letters).

This represents any (Y.wye.star) connected winding, regardless if primary or secondary.

In case of a zig-zag winding, each coil is divided into 2 parts (let's call them A1 and A2, ...).

The second diagram shown in Simon's response represents this connection. Basically, the voltage for phase A there is obtained by adding the voltages A1-C2, B1-A2 and C1-B2, where A1, B1,C1 are the first half-coils on the respective legs while A2,B2,C2 are the second half-coils on the same legs. The sign minus (-) denotes that that coil is connected in opposite direction (output of A1 connected to output of C2).

There are a lot of web sites about transformers, at different levels. Just type in "Zig-zag transformer diagram). One of them is this (diagrams on page 45)

Power Quality in Power Systems and Electrical Machines - Google Books Result

by Ewald F. Fuchs, Mohammad A. S. Masoum - 2008 - Technology & Engineering - 638 pages
Problem 1.3: Current Phasor Diagrams of a Three-Phase Transformer in Delta/Zigzag Connection With Line-To-Line Load The delta/zigzag, three-phase ...
books.google.com/books?isbn=0123695368...

__________________
Scientes et audaces fortuna juvat !
Register to Reply
Associate

Join Date: May 2009
Posts: 32
#7
In reply to #6

Re: Zig Zag Transformer

06/03/2009 2:51 PM

Thanks Sir Thanks A lot for helping me, if you don't mind may I ask u more doubt about transformers after checking google link

Register to Reply
Anonymous Poster
#9
In reply to #3

Re: Zig Zag Transformer

08/14/2010 4:21 AM

Simon,

you are connect.Zig Zag winding connection is used in order to increase the impedence of the system.

This transformer has two windings

connections such as ZnYn11.

Register to Reply Off Topic (Score 5)
Anonymous Poster
#10
In reply to #9

Re: Zig Zag Transformer

08/14/2010 4:23 AM

sorry .. the correct is wrongly spelled

Register to Reply Off Topic (Score 5)
Associate

Join Date: May 2009
Posts: 32
#4
In reply to #2

Re: Zig Zag Transformer

06/03/2009 12:35 PM

sir thanks for your information, but its a bit difficult for me to understand, can you please explain me this in a simple way with a simple digram.

Regards

JK

Register to Reply
Anonymous Poster
#8

Re: Zig Zag Transformer

08/14/2010 4:17 AM

Zig Zag connection is used in order to increase the impedence .This connection is mostly used in earthing transformers.As you know that the earthing transformers are used where the network length is small.

Also this kind of winding can supply additional KVA than the normal rated , ie it can have two kVA rating .The second KVA rating will be for a short duration which will be existing under fault condition.

ex. connection such as ZnYn11 is used

Register to Reply Off Topic (Score 5)
Register to Reply 10 comments

"Almost" Good Answers: