Disconnecting Ammeters from Current Transformers

05/29/2009 12:47 AM

What are the steps that would take before disconnecting ammeter permanently supplied from a current transformer?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: How to disconnec ammeter permanently supplied from a current transformer?

05/29/2009 1:49 AM

Well short-circuiting the CT to prevent accidental open-circuiting of the CT output would be a good start.

__________________
jack of all trades
Register to Reply Score 1 for Good Answer
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#2

Re: How to disconnect ammeter permanently supplied from a current transformer?

05/29/2009 1:50 AM

Switch 'OFF" the power supply before you disconnect the ammeter or short circuit the current transformer.

Don't dismantle out the ammeter with the current transformer loaded other wise your CT will burnt down.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: How to disconnect ammeter permanently supplied from a current transformer?

05/29/2009 3:07 AM

<...Don't dismantle out the ammeter with the current transformer loaded other wise your CT will burnt down....>

This assumes that the individual disconnecting it hasn't died from electric shock first!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: May 2009
Location: Philippines
Posts: 23
#4

Re: How to disconnec ammeter permanently supplied from a current transformer?

05/29/2009 3:10 AM

What are the steps that would take before disconnecting ammeter permanently supplied from a current transformer?

I would suggest 1) switch "off" the power supply 2) install terminal block suitable to the size of CT wiring 3) disconnect the two wires from the CT and re-connect it to the new terminal block 4) install jumper wire across these two CT wiring to short it out, or you can also connect the two CT wires in a single terminal in the terminal block 5) or you can connect jumper wire across CT secondary terminals. NOTE: make sure CT is not open circuited when power is "on", otherwise, high voltage will be present in the CT.

regards.

rudy c. fernando

Register to Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#5

Re: How to disconnec ammeter permanently supplied from a current transformer?

05/29/2009 8:55 AM

roshanrrd; note: your removed AC ammeter would typically be 0-5 amps full scale. perry

Register to Reply
Guru
Technical Fields - Architecture - New Member Popular Science - Weaponology - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - Hunting - New Member

Join Date: Dec 2005
Location: Clemson, South Carolina
Posts: 1722
Good Answers: 18
#6

Re: How to disconnec ammeter permanently supplied from a current transformer?

05/29/2009 9:00 AM

I'm surprised that no one has asked, "Why?"

__________________
We have met the enemy and he is us . . . Walt Kelly
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#7
In reply to #6

Re: How to disconnec ammeter permanently supplied from a current transformer?

05/29/2009 9:16 AM

<Sarcasm>

Because the feeder being fed from the source that the CT/meter is watching is overloaded and if we remove the meter the problem goes away.

</Sarcasm>

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#8
In reply to #6

Re: How to disconnec ammeter permanently supplied from a current transformer?

05/30/2009 2:28 AM

Maintenance on a powered line perhaps? It is safe to play with the output of a live CT if you cannot wait until the power can be shut off (such as a substation CT), as long as you take adequate precautions.

__________________
jack of all trades
Register to Reply
Anonymous Poster
#9

Re: Disconnecting Ammeters from Current Transformers

05/30/2009 10:42 AM

sometimes ammeter should be removed with out switching off the power supply.in that case short circuit the secondary of ct.there will normally be provision for that.short circuiting the ct secondary is not a great problem as ammeter itself is offering only a very low resistance path.

then disconnect and remove the ammeter.

Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#10

Re: Disconnecting Ammeters from Current Transformers

05/31/2009 10:08 PM

Roshanrrd,

As others have said a number of times, short the two CT secondary leads together. I know that in electrical work one normally thinks of a short circuit as a thing to be avoided. But here is the reason:

  • The CT can be thought of a power supply capable of providing as much voltage (or as little voltage) as is needed to drive a given current through its output load. Thus it is current limiting, but not voltage limiting.
  • Its output current is proportional to the current flowing through the conductor it surrounds.
  • In the most common applications its secondary current will be in the range of 0-5A.

Now, if the load resistance is 5 ohms, the power it is producing is as much as 25watts. As you decrease the load resistance towards 0 ohms, the voltage across the terminals will decrease towards 0 because it is inherently current-limiting. If, on the other hand, you open the circuit, it will output a potential across the terminals that can approach the insulation breakdown voltage of the wires in the CT, and/or damage the CT in other ways so it no longer can provide an accurate proportional output when it is reconnected. So, yes, short its two terminals together before you disconnect any load meter, always. There usually will be jumpers on the terminal strip to allow this to be done without disconnecting any leads. Leave the shorting jumper in place until after the load meter is connected, always, even if it is on a de-energized circuit.

--JMM

Register to Reply
Associate

Join Date: Apr 2008
Location: 66°N (almost)
Posts: 46
Good Answers: 1
#11

Re: Disconnecting Ammeters from Current Transformers

06/01/2009 7:13 AM

Best way is to switch of power first, then disconnect and shortcircuit the trafo before you switch on power again.

It is essential to short circuit the trafo, If you can do it without disconnecting first than it is ok, fex. if there are two connection screws on each end on the trafo

__________________
It is no use saying, 'We are doing our best.' You have got to succeed in doing what is necessary. Winston Churchill
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member

Join Date: May 2008
Location: CHENNAI, TAMIL NADU, INDIA.
Posts: 1851
Good Answers: 65
#12

Re: Disconnecting Ammeters from Current Transformers

10/05/2009 1:11 PM

Dear Mr.Roshanrrd,

You can use a test block installed before you open the terminals of tha Ammeter so that it is safe. Or else the voltage will be multiplied by the ratio of the Current transformer, leading to explosion or burning out of Current Transformer, or cause severe shock to the staff.

DHAYANANDHAN.S,

CR4 MEMBER,

INDIA.

Register to Reply
Register to Reply 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Bill (1); dhayanandhan (1); jack of all trades (2); jangkly (1); jmueller (1); North of 60 (1); perry (1); PWSlack (1); rudy_fernando5r (1); Simon Wan (1)

Previous in Forum: Zig Zag Transformer   Next in Forum: Software for Capacitor Placement

Advertisement