Engineer

06/02/2009 7:40 AM

can we make shart neutral of 2 different load which supplying bye deffrent source

thanks

Register to Reply
Pathfinder Tags: smr.7189@gmail.com
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Engineer

06/02/2009 7:42 AM

shart shared neutral.

Neutral is simply the star point of the local distribution transformer, which is earthed at that place.

If there is a set of cables coming in from the second supply, is there no neutral in them?

If there isn't, then why is a neutral needed from the second supply?

Please share the installation in greater detail for the forum.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#2

Re: Engineer

06/02/2009 9:28 PM

Definitely No,

It is NOT recommended to share the neutral point with other power supply load of different source. Each Transformer has it own neutral point. No doubts, each transformer neutral is earthed to the ground, it doesn't mean that both grounding are having the same impendence

The other problem is to prevent the leakage current from the other load flowing in to this load.

For Example; If your 1st transformer load having a high leakage current and your system does not trip, then, the high leakage current will flow to the 2nd transformer neutral system and cause unnecessary tripping to this transformer.