Anonymous Poster

Motor Conection for VFD Application

06/03/2009 5:02 AM

Dear All

I was commissioning a 3.7KW VFD(AC drive) for a tooling machine in X-axis( X-axis had two tools attached and used for Boring application)

Motor Connected was 415V Delta, 6 terminal motor, 7.5 amps (As per nameplate). But when I went with the trials Drive was tripping with Overcurrent in less that a 1/4 of a second after Run command.(Motor taking 15 Amp)

Then we connected the motor in Star and guess what application is done successfully.(Motor taking 2 Amps)

How the change in motor connection has worked? I kept the voltage rating of the motor 415V same in the drive for both cases.What effect it will have on torque?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Motor Conection for VFD application

06/03/2009 6:24 AM

Check the links inside the motor terminal cover for the correct connection arrangement in delta. It sounds as though one of the windings could be reversed.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Motor Conection for VFD Application

06/03/2009 4:31 PM

I believe it's normal for an IEC 6 lead dual voltage motor to use the Delta winding pattern for the lower voltage, i.e. 240V, and the Star winding pattern for the higher voltage, i.e. 415V. Sounds to me as though you had it hooked up wrong the first time.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#3

Re: Motor Conection for VFD Application

06/04/2009 5:17 AM

If the motor is drawing too much current (it is!!) then this is either misconnection or you are applying too much voltage.

Other posts recommend connections check etc, also set the VFD to a simple v/f control and set the starting voltage to its minimum setting with a 5 second acceleration time to see if this reduces this current. Working better in star seems to imply your voltage is too high causing the problem.

I take it that the motor is a 50Hz winding, if not, change the rated voltage and frequency in the VFD to the motor nameplate.

__________________
Something new every day!
Reply
Anonymous Poster
#4
In reply to #3

Re: Motor Conection for VFD Application

06/04/2009 6:14 AM

Dear all

yes the motor has 50Hz winding, and there is no question of misconnection as it is running ok in star.

Thing i want to know is should i lower the voltage entered in drive for star? ( currently it is 415V) What about torque ? well the running frequency for this application will be max 3 Hz.

Reply
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#5
In reply to #4

Re: Motor Conection for VFD Application

06/04/2009 6:56 AM

The VFD has a motor rated voltage and frequency etc (415V and 50Hz, 7,5Aflc delta).

Your motor should be connected for delta, the 415V connection.

Also, you can programme the starting voltage, sometimes called 'boost' - this is the parameter you need to adjust to a lower value. What VFD is it?

3Hz is quite low for some inverters, this is normally better in 'automatic' control, letting the inverter change the voltage applied to keep the motor current correct for the actual load.

However, you should still be able to get a reasonable result at this Hz unless the load is high but I guess you're just trying to get it going in no load at the moment.

__________________
Something new every day!
Reply