Flow Valve

06/04/2009 3:21 AM

Normally control valve with I/P have, One Digital input(DI) from the Switch and one Digital output(DO) going to Solinoid and one Analog output(AO) which is going to I/P converter to operate the valve.

But In my case Control valve with I/P have only Analog output. Swithes are not compulsary for control valve or required

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Flow Valve

06/04/2009 3:30 AM

Then the switches' inputs cannot be connected up.

If the software is a standard subroutine that must be used regardless, maybe because of Client specifications, then arrange for 0% output signal and 100% output signals to drive the bits that say "fully closed" and "fully open", whichever way round they are. There isn't anything else to be done.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856