Monitoring Furnace Glow Bars

11/29/2006 6:29 PM

I am doing a project on a furnace and one of the things i want to do is to be able to monitor the glow bars incase they break there are 8 glow bars that are pulling about 60 amps at 240 volts. and thay are paired in 2s so i know i can read a voltage drop across the two . but i need a Convertor with at lest 8 to 12 inputs and outputs that can convert the 240 volts AC to 120 volts AC or Convert it to low Voltage DC with a limited amount of space . then the output of the Convertor will go to an AllenBradly PLC.

Thanks

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jan 2006
Location: Australia
Posts: 269
Good Answers: 1
#1

Re: Monitoring Furnace Glow Bars

12/01/2006 1:11 AM

Can't you put current clamp transducers on the supply cables and monitor the current draw? You should have no problem getting a transducer to read 60 or 120 amps AC and give you a 4 - 20ma signal for your PLC

__________________
An engineer is a man who can do for five bob what any bloody fool can do for a quid (Neville Shute)
Register to Reply
Power-User

Join Date: Dec 2005
Posts: 200
Good Answers: 8
#2

Re: Monitoring Furnace Glow Bars

12/01/2006 3:03 AM

Standard practice is to use a safe, reliable, low cost instrument transmitter or hockey puck for each input/output (I/O) to the AB PLC.

AB PLC powers each transmitter with say 24 VDC.

Transmitter Output signal is 4-20madc.

Zero output represents circuit failure.

20 madc represents max signal

4 madc represents min signal.

Calibration is users choice.

AB PLC can be programmed to read out current, voltage, watts for each circuit, all circuits combined, or any combination of interest.

__________________
Corn Stoves
Register to Reply
Participant

Join Date: Nov 2006
Posts: 2
#4
In reply to #2

Re: Monitoring Furnace Glow Bars

12/01/2006 7:56 PM

How much Heat can the transmitters take. where i would have to mount them is about 1000 degrees C

Thanks for the help

Register to Reply
Power-User

Join Date: Dec 2005
Posts: 200
Good Answers: 8
#5
In reply to #4

Re: Monitoring Furnace Glow Bars

12/02/2006 3:33 AM

Are there any other surprises in addition to the ambient temp of 1000 deg C?

Mount the transmitters at the power source.

If you insist for no good reason to mount electronic devices inside a boiler, first check with your psychologists, and secondly use exair (see www.exair.com) coolers.

__________________
Corn Stoves
Register to Reply
Anonymous Poster
#3

Re: Monitoring Furnace Glow Bars

12/01/2006 5:26 PM

How about indicating fuses across the bars.

An open bar will trip the fuse and provide failure indication

via a switch from the fuse holder to your control circuit.

It's old tech, but it works, - cheap too.

Register to Reply
Register to Reply 5 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); Cornstoves (2); krypton1592 (1); nutwood (1)

Previous in Forum: Sensing Pressure in IV Lines   Next in Forum: Underground Electricity
You might be interested in: Furnace Controllers, Heating Furnaces, Igniters

Advertisement