Underground Electricity

11/30/2006 2:23 PM

What is the maximum distance to run electric underground from the power pole to a building. The building would be a garage with 220V. The largest draw will be a table saw or small welder. What size of wire would be needed.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Underground Electricity

11/30/2006 11:57 PM

you would have to know how much current you will be drawing. then depending on the distance you will want to compensate with the correct gauge wiring. larger gauges are more expensive but allow for less resistance, inturn a smaller voltage drop across your AC line. look up a wire gauge table.

Reply
Anonymous Poster
#2

Re: Underground Electricity

12/01/2006 12:47 AM

16mm x 1200meters

Reply
Power-User

Join Date: Dec 2005
Posts: 200
Good Answers: 8
#3

Re: Underground Electricity

12/01/2006 2:52 AM

Theoratically there is no limit to the length of underground electrical cable.

An aboveground junction box is required at the end of each roll of electrical wire. Underground splices are not allowed and would be rather unwise.

__________________
Corn Stoves
Reply
Anonymous Poster
#4

Re: Underground Electricity

12/01/2006 3:57 AM

The bigger the conductor area the smaller the voltage drop. If the cable is too small than the cable itself will become the circuit protective device (a "fuse"), in which case it will need digging up and replacing every time it blows, assuming it doesn't cause collateral damage or hurt someone in so doing...

Reply
Power-User

Join Date: Nov 2006
Location: antwerp/belgium/europe
Posts: 160
Good Answers: 5
#5
In reply to #4

Re: Underground Electricity

12/01/2006 5:09 AM

This question was more or less asked in another thread. Fill in your data in the formulas. These formulas are made with the percentage of power loss in mind.

Ud = voltage drop
UL = line voltage
I = current
R = total resistance of cable
L = lenght cable
ρ (rho) = resistance per meter per square milimeter of copper wire (0,0175)
a = diameter (in mm²) of cable.

UL = 400V, I = 63A, L=630m

Ud = 400 x 4%

Ud = I x R

Ud = 63 x R

Ud = UL x 4%

R = (L x ρ) / a

UL x 0,04 = I x (L x ρ) / a

a x UL x 0,04 = I x L x ρ

a = I x (L x ρ) / UL x 4%

a = 63 x 630 x 0,0175 / 400 x 0,04

a = 63 x 11,O25 / 16

a = 43 mm² > in reality : 50 mm²

you need a cable of 4 x 50 mm² to run your motor(s)

__________________
44mEurope
Reply
Anonymous Poster
#6
In reply to #5

Re: Underground Electricity

05/25/2007 9:39 AM

are these all of the materials you need

Reply