i need some help. if you send me latest design/drawing of 11KV Automatic Changover switch, i will very thank full to you. it will helpfull for me, you know taht ATS module are usualy use for Main AC & Generator, but in this case both supply are A.C Supply Form different Grid Station. And in ATS OR AMF Module DC Supply 12VDC OR 24VDC is necessary for operation. But in this case we have no Battery supply.
What is solution of this problem & which type of PLC/Module will suitable for this Circuit.
Kindly Send me Breaf Answer and Design
Thnanks.
Best Regards!
Waseem
Re: 11KV Automatic chngeover Switch
06/09/2009 11:26 AM
Quote "if you send me latest design/drawing of 11KV Automatic Changover switch".
You can forget that. Suggest you get to work and Google "11KV automatic transfer switch" There is plenty of information available.
Re: 11-KV Automatic Changeover Switch
06/09/2009 3:32 PM
Try looking at existing automatic transfer switches on the market.
http://www.sandc.com/default.asp
I have worked with these and they are not a simple project the average consultant can design and build by any means. Perhaps you should leave it to the experts and just specify a pre-designed, pre-tested and pre-built one.
06/09/2009 11:01 PM
Hello Waseem,
You have not specified what is the nature and amount of the load that you are wanting to transfer. Is it critical (cannot afford any break at all) ? Does it have static loads or induction motor loads ?
We manufacture automatic fast bus transfer systems (www.aartechsolonics.com) and can work with you to scope out your requirement. There are a lot of solutions out there in the market suiting different applications and one will have to be more specific.
Best, Amit.
06/10/2009 3:23 AM
Hell Amit Sb!
I need help For 11KV VCB Switchgear, So I need Solution of atomatic Changeover switch which will be made with 2 11KV Vacuum Circuit Breaker. 630A load
thaks
waseem
06/10/2009 6:14 AM
The source change-over may be done using hardwired relays or a controller. The design will depend on the 11kV switchgear intended to be used. Considerations for the controls include auto / manual switch, voltage sensing relays, position and status indicators, interlocking - mechanical and electrical, adjustable time delays for transition and interface to the 11kV switchgear trip / close circuits.
If a DC supply is not available, the source change-over circuits should be supplied from either external ac source or from voltage transformers on the 11kV source circuits. It is likely the 11kV trip / close circuits will be DC.
Hope this give some guidance.
06/26/2009 7:59 AM
You will have contact Cummins Power Beneration Business Unit, Power Electronics Department.
Regards
Pravin