Neutral CT Specs

06/09/2009 6:52 AM

Can anybody help me for selection of Neutral CT specification for Star wound primary & Start wound seconday of Transformer.

Transformer rating id 40 MVA, 220 kV 11 kV. Means Primary rated current = 105 amps & Sec rated current = 2100 amps.

220 kV side & 11 kV Side neutral is Solidy Earthed.

I want to fix Neutral CT in both primary & Seconday neutral for REF (64) protection & Stand by Earht fault (51G, 50G) protection for Transformer.

I want to know what should be CT Ratios for both the type of protections & What is reason behind it?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Neutral CT Specs

06/09/2009 3:38 PM

Have a look at previous threads on CR4 on this subject for the answers. To start you off, your CT ratio depends on what protection device the CT is being connected to. Look in the data sheets of said protection device(s) and it will tell you what the ratio of the secondary side of the CT needs to be.

__________________
jack of all trades
Register to Reply
Anonymous Poster
#2

Re: Neutral CT Specs

06/10/2009 4:24 AM

hi

for that u need to first calculate earth fault current at primary and at secondary too.

and CT mustnot get saturated at that fault current, so accuracy class must be so pricise, which can withstand high fault current with keeping its secondary current with in limit,

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Neutral CT Specs

06/19/2023 6:06 AM

Surely a telephone discussion with the <...Transformer...> manufacturer is quicker than waiting for CR4?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 3 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); jack of all trades (1); PWSlack (1)

Previous in Forum: How Does Cross-Current Compensation in Parallel Generators Work?   Next in Forum: 11-KV Automatic Changeover Switch

Advertisement