Diesel Generators and Synchronization Problems

06/10/2009 8:53 AM

Hi,

I am new to this website, and I would like to ask anyone out there who has experience with generator synchronizing problems that I have encountered recently.

1. Background

We have a two 350KVA diesel powered generators operating in paralllel as emergency backup system. The control system cards from GAC ( Governors America Corp ) such as Speed control unit (ESD 52000 series ) , Load Sharing Module (LSM 672) and Synchronizer (SYC 6714) are at least 15 years old in use.

lately i am facing a technical problem, in that there is a reverse power tripping on always on second generator. Normally the reverse power set point setting is around 10 percent of the generator rating (approx 28kw). I have fine tuned and adjusted the bias setting of the engine governing system for both generators and it appeared to worked for a short while for a week or so.

But the problem repeated after running for one week and apparently we dont know what is/are the root causes of the tripping.

The reverse power now is running a tune of more than 10 percent and its tripping very often when we start the system.

I do not know which of the 3 cards is causing the problem, perhaps a combination problem? as the cards are linked to one another.

Would appreciate if anyone out there would share their experiences on this type of problem.

Thank You.

Minsaram

Register to Reply
Pathfinder Tags: synchronisation
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Diesel Generators and Synchronization Problems

06/11/2009 5:22 AM

Sounds like a governor problem, perhaps caused by the load sharing controller.

If One Alternator trips out on reverse power, and you can establish that the alternator did in fact experience reverse power, IE the alternator motorized, then obviously the on line alternator has assumed the load.

Observe the power factor meter or KVARS meter, the alternator experiencing reverse power will show leading power factor or VARS.

Also notice the frequency of both alternators when the reverse power relay trips. a moderate or large difference between the on line and off line alternators will indicate speed governor control problem. The on line frequency may rise significantly (5 Hz is significant). The off line alternator frequency will likely rise some when taken off line. if the off line alternator frequency drops significantly, check the governor or fuel system.

A really simple to fix problem I have encountered with electronically controlled governors in which the speed is sensed with a magnetic pickup on the flywheel ring gear (IE counting the # of gear teeth passing the pickup), has been small shards of iron likely from starter gear engagement/disengagement collecting on the magnetic pickup and degrading the signal from the pickup (Typically around 7 volts AC, 2-3 Khz).

I suggest that you remove the mag pickup carefully noting exactly how far it is inserted, I have marked the barrel of the pickup, locknut, and bell housing with a marker to be able to return it to exactly the same insertion depth. Or refer to manufacturers recommendations for proper insertion.

If shards of iron are found on the mag pickup clean it thoroughly, this may take some effort as the iron shards will resist removal from the usually quite strong magnet.

The bell housing should be cleaned as best as possible with compressed air and/ or power washer, rags etc, whatever you can get in to the bell housing to remove debris.

Some Caterpillar engines mount the mag pickup on the camshaft gear housing, however they too are not immune to fouling by small iron particles that may circulate in the lube oil (Indicates a more serious issue).

Have you had the oil analyzed for contaminants, could save you a nasty surprise.

Regards CEKM

Register to Reply
Member

Join Date: Jun 2009
Posts: 5
#6
In reply to #1

Re: Diesel Generators and Synchronization Problems

06/15/2009 10:03 PM

Hi All,

Thank you very much for the various inputs and insights I received from all of u thus far; These are the answers to the above questions asked by the various participants.

1. Have replaced the Generator 2 governor with Generator 1 governor, problem still remains i.e. the reverse power problem is still encountered.

2. Cleaned up the magnetic pick up of any magentic debris or contaminants, problem doesn't disappear.

3. The fuel is coming from the same tank to both the generators and the fuel is not contaminated

4. Carried out the load test individually on the Gen set, and discovered there is no problem in frequency, voltage or amperage. There is also no Hunting on the generator. Good stability is observed.

5. Tried to swap Load Sharing Module and Synchronizer cards with used cards, problem still persist.

Regards

Minsaram

Register to Reply
Guru

Join Date: Jul 2008
Location: Mallorca, Spain
Posts: 567
Good Answers: 15
#2

Re: Diesel Generators and Synchronization Problems

06/11/2009 8:56 PM

If you have the original set up procedure in the manual or can get it on line, start from the beginning and set up from scratch. Don't tweak or fiddle, set them up in the same order as the book says. In fifteen years some of the components have probably drifted out of tolerance but not necessarily failed.

I don't think it will be the synchronizer as this is, I believe, only responsible for the initial paralleling of the sets

regards

Chas

__________________
En la casa del herrero, cuchillos de palo!
Register to Reply
Power-User
Hobbies - HAM Radio - New Member

Join Date: Oct 2008
Location: Houston, Texas
Posts: 252
Good Answers: 5
#3

Re: Diesel Generators and Synchronization Problems

06/12/2009 12:22 AM

Check the AVR, exciter system, PTs, CTs and protection relays. Loss of excitation and metering problems can also cause reverse power trips. The problem could be and probably is intermittent. Been there chased that goose! Got pinched and wing whipped a few times too!

TT3

__________________
If the software can detect, compensate, avoid, or correct an anomalous condition in the system, it is, by definition, a software problem-regardless of the root cause. In the long run, for most classes of problems, it is cheaper to fix it in the SW
Register to Reply
Power-User
Turkey - Member - New Member

Join Date: Mar 2007
Posts: 310
#4

Re: Diesel Generators and Synchronization Problems

06/12/2009 12:55 PM

what if a diesel generator works no-load regarding frequency? it is 60 hz or something like 62 hz? İ also know that a generator will have a slightly higher voltage than nominal while working no-load so why? if it has both AVR and frequency controller it doesnt make sense all right? i dont know reality i just guess pls englihten me..

__________________
jinxnao
Register to Reply
Guru

Join Date: Jul 2008
Location: Mallorca, Spain
Posts: 567
Good Answers: 15
#5

Re: Diesel Generators and Synchronization Problems

06/12/2009 2:21 PM

Hi Minsaram,

Just a thought, Have you checked the fuel itself? If they are running from separate tanks you could have a contamination problem. How about air in fuel?

The fact that you improved the issue by adjusting the governor setting doesn't mean that it is a control system fault, it could be mechanics. Can you run the second gen on its own at full load for a test? that would eliminate fuel /fuel system problems.

regards

Chas

__________________
En la casa del herrero, cuchillos de palo!
Register to Reply
Anonymous Poster
#7

Re: Diesel Generators and Synchronization Problems

06/16/2009 3:04 AM

Minisaram,

I too have had these kind of problems that didn't make sense, and spent lots of time chasing intermittent problems.

I suggest that you go to a Refrigeration wholesaler and get what are called "Tattletales", small inexpensive devises available in 24, 120, and 220 volt versions, attach them across the contacts of suspected components, the devices will burn a small wire giving visible indication that the contact has opened, has worked for me in chasing down phantom events.

Also check the tightness of every screw and connection in the system, pull on every wire to ensure connection is tight.

Was on a ship about to depart, Emergency generator would start, then immediately die. Illegal for the ship to depart without a functioning EDG. Chief and 1st assistant were about to begin the procedure to replace and calibrate the digital governor control, a two hour job, tugboats were alongside, Pilot on board.

I persisted in pursuing the KISS approach Keep It Simple Stupid, I opened junction boxes and started pulling wires in one box I pulled on a wire connecting the Mag pickup to the governor, out it came from the crimp ring connector, two other similar improperly crimped connections were found.

We made the departure on time.

Moral, look at the simple things first It ran fine previously right?

Good luck

CEKM