Hi there.
I am using a 12VDc to 220 VAc Inverter to supply a load that needs 2A to operate.
The inverter was working perfectly for a very long time (more than a year) but for a while now, it is still working perfectly with out the load.
Once the load is connected, it is still working for a couple of time (30min) and after, the output voltage (Ac) drops to less than 10VAc.
I am wondering what could be wrong.
Any help will be grateful.
Yours faithfully.
Nganpet.
Impossible n'est pas Camerounais
Re: DC to AC Inverter
06/10/2009 8:51 AM
What is the make of the inverter?
What is its output rating?
06/10/2009 8:56 AM
The make is COTEK and its output rating is 210-230VAc
06/10/2009 9:09 AM
That's its voltage. Can it raise 2A at that voltage continuously under normal operation, i.e. support a 450W load - is it rated at that, or is it being over-driven?
The reason for the question is that many inverters have some form of overload protection on them that will shut the thing off if the burden on them is too heavy. And no-one can see it from here.
Good Answers: 18
06/10/2009 9:15 AM
And the rated power or rated amps???
Good Answers: 103
06/10/2009 9:41 AM
Is the storage battery OK? after 30 minutes check the voltage at the battery end.
Otherwise I don't see any problem other than some IC getting overheated and blocking off as mentioned in a previous post.
Never faced this problem with inverters but now facing with my TV, that used to sleep after some time, some Ic of the tuner was overheating.
Good Answers: 73
06/10/2009 9:42 AM
Have you checked your 12VDC source? Perhaps it is worn out???
Good Answers: 53
06/10/2009 12:32 PM
Its battery is gone for sure,
06/10/2009 11:03 PM
Some inverters require a resistive or inductor (transformer) load.
As others have mentioned if the load is too small or too great or the power factor outside limits the inverter output can collapse.
If the input voltage or available current is too low, output can collapse.
"I believe we are masters of our lives - we hold all the cards and it is up to us to use them right." Vesna Vulova - survived 33,000ft fall
06/11/2009 12:17 AM
HI DEAR
I didnt work on the inverters before but let me tell you the reason why the output trip when you connected it to load the transisters which is present in the circuit board i think its D138 change those all and you will nt see that problem again in ur inverter thats the last solution but first you will have to go for the others suggestion okz if it works then do let us inform
REGURDS
FARRUKH ADNAN
SUPPORT ENGINEER
NOYHING AS IT SEEMS AS IT APPEARS TO BE
Hobbies - Musician - New Member Hobbies - Car Customizing - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member
06/11/2009 6:44 AM
Does the output come back immediatly after removing the load or after a cool down period?
If it comes back immediately it sounds as if it may not like the load you have on it, poor power factor, maybe. If it takes a while to come back it sounds more like a thermal issue. What is the ambiient temperature where you are operating it?
Does it have adequite airflow when it is operating? It it getting hot externally when it quits or does it seem normal?
Could be a cold solder joint, I see that issue quite a lot anymore.
Just my random thoughts on the matter.
Good Answers: 150
06/11/2009 9:18 AM
Some things that you should look at:
You should probably open the case up and blow all the dust bunnies and crud out of the heat sinks and make sure all the fans are turning easily. if they aren't turning easily, the wax that many chinese manufacturers have mistaken for grease has probably hardened and turned into glue. Get some electrical contact cleaner spray and flush all the gummy crud out of the bearings, allow it to dry, then spray the bearings with spray teflon lube and let it dry.
If you do that and it does not help. you may have electrolytic capacitors that have aged and dried out and are allowing more ripple current to leak through. This will cause the system to overheat which will dry the caps out even more, which will cause more heating... it is a viscious cycle. try replacing the aluminum electrolytic caps with new ones.
If that does not help, then you probably have a resistor in the overload trip circuit that has changed value due to heating. This is common for carbon composite resistors but not so common for metal film resistors. You'll need to check the resistance of each one against the color code or labeled value. replace the resistor(s) that are out of tolerance with a non-inductive metal film resistor of the same value and tolerance. This step may need to be done by the manufacturer since there may be some trimming and tuning required for proper operation. A prior poster indicated a specific resistor that might be the problem, I gather he is intimately familiar with that particular unit.
Who is John Galt?