Transformer Impedance and kVAr Compensation

06/11/2009 12:20 PM

For calculating Transformer Impedence compenseting KVAR of 2000KVA Transformer

Transformer rating is 2000 KVA

Impedence of the transformer is : 6.25% (As per the vendor)

Let X be the total load in KW

So total load in KVA = KW/ P.F

Intial P.F is 0.8

Improved P.F should be = 0.99

Can any one let me know what is the base formula for calculating Transformer Impedence compenseting in KVAR

Transformer Impedence

compenseting in KVAR = =Square of loading of trans X %Z X Rating of Trans

Could any one the basic of the formula where it is derived from.


------------------------------------------------------------------------------------

%Z
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Transformer Impedance and kVAr Compensation

06/11/2009 8:23 PM

You need to add load to the transformer first. Your caps are installed to correct the load and not the transformer to the power factor you want.

Register to Reply
Anonymous Poster
#2

Re: Transformer Impedance and kVAr Compensation

06/15/2009 1:57 PM

Be careful correcting the transformer power factor to above 95%. You always want to remain in a lagging power factor. If you go past 100% you are in a leading power factor. The load determines power factor and loads can change as they switch on and off. good luck

Register to Reply