steam surface condenser

06/14/2009 2:03 AM

I want to ask about the turndown ratio of water cooled steam surface condenser & how it is calculated. Generally how much minimum turndown ratio is allowable for the water cooled steam surface condenser

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: steam surface condenser

06/15/2009 3:42 AM

Generally the things will operate down to zero throughput.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User

Join Date: Mar 2009
Location: O'er looking the silvery Tay
Posts: 255
Good Answers: 18
#2

Re: steam surface condenser

06/19/2009 12:11 PM

Hi,

Yes; there really is no limit to the turn-diwn;the big question is what type of arrangements you have for the condense side as water hammer can become a problem as the steam flow rate reduces.

Basically you want the condensate to drain freely from the heat exchanger surfaces without water logging occurring as when this happens the incoming steam can react concussively with the water. If you are working into a vacuum then the chances are very good that the surfaces will remain free from stagnant water; whereas if you are using the steam pressure to force the condensate back through the return pipework then waterlogging is virtually guaranteed to happen.

Some installations avoid this occurring by the use of an air admittance valve above the steam inlet which avoids a vacuum developing whilst the condense is taken by gravity to an atmospheric pressure hot well via a simple float trap. This also permits the heat exchanger to remain free of accumulated condensate; with this arrangement you either dump the condensate, gravity drain it back to the boiler or pump it.

Clearly you must plan the position of the steam and condense pipe work carefully to avoid creating a situation which prevents natural clearance of the water.

Hope this helps.