impulse tubing

06/14/2009 10:00 PM

Hi All,

why do they required the installation of lead to be slope down.

i.e flow & pressure transmittter.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#1

Re: impulse tubing

06/14/2009 10:29 PM

Hi ronron,

Sloped down from what and to what?

(more info would help a lot)

Mike

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply
Anonymous Poster
#2

Re: impulse tubing

06/15/2009 12:06 AM

For achieving better accuracy & perfomance. That's why we maintaining slopdown for gas or liquid service

Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#3

Re: impulse tubing

06/15/2009 12:08 AM

It is not only sloping down, we prefer them on the lower side of the pipeline too (approx at 90 deg position) to aviid the air bubbles from entering the tube and disturbing my readings if that is what you mean. But then again at the end (if it the impulse tubing terminates at a cabinate) it goes up and at the highest point we put a vent valve.

Guessing If this is what you mean.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Commentator

Join Date: Mar 2009
Posts: 61
Good Answers: 3
#4

Re: impulse tubing

06/16/2009 7:15 AM

I am assuming that by "lead" you are referring to the impulse tubing used with pressure and pressure differential transmitters (PDTs, LTs, FTs etc.).

The slope is required especially for gas or vapour services which are mounted above the tapping points in order to ensure that any condensate build-up (which is inevitable) will drain back into the pipe and not remain in the impulse lines and sensor housing and act on the sensor therefore creating inaccurate differential pressure readings.

API-RP-551 Section 2.3.2.2 states; "A positive slope, at least 1:12 for all leads, should be provided."

Register to Reply Score 1 for Good Answer
Associate

Join Date: Jan 2007
Posts: 35
Good Answers: 1
#5

Re: impulse tubing

06/17/2009 2:42 AM

The slope is provided for better draining/venting of impulse lines and also to avoid any liquid/vapour pockets in the impulse lines which will affect the correctness of measurement.

R.Thiyagarajan

Register to Reply
Anonymous Poster
#6

Re: impulse tubing

06/20/2009 9:18 PM

for liquids, the measuring device should be lower than the source.For gases, it should be higher,except for steam, which should be lower or have a pig-tail fitting to trap liquid.Basically, no liquid in a gas measuring line, no vapor in a liquid measuring line.Simple,eh?

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!