Anonymous Poster

KWH Reading Difference

06/22/2009 5:02 AM

Hello expert,

Need your help to determine the power loss in power transformer and convert it into KWH ,

In the other word, is there any significant difference of KWH reading if we put the KWH meter in Medium Voltage side (Usually KWH installed in Low voltage side)

I do understand that if we put the KWH meter in medium side (20 KV) the energy used by power step down transformer (20 KV to 400 V) will be counted by KWH meter. How significant the difference of KWH reading if the transformer rating is 1250 KVA and loaded 50 % in average?

Thank you

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: KWH reading Difference

06/22/2009 5:04 AM

The difference between the two readings will be the heat that is dissipated within the transformer.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#2

Re: KWH reading Difference

06/22/2009 5:43 AM

Note that the efficiency of a transformer will generally be at its highest (typically ≈95%) when fully loaded. At 50% loading, it may be down to ≈75%.

So to answer your question, there will almost certainly be a significant difference.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#3

Re: KWH Reading Difference

06/22/2009 2:25 PM

It is not a problem to get accurate metering on the low side of the transformers. The method is to use metering that can be programmed with "compensation" factors to account for the transformer losses.

There are several good reasons to use compensated metering, primarily cost of equipment and safety. No meter will be handling 20kV, so there will be an expensive voltage transformer with it's own factors needed on the high side. Both sides will require CT's (Current Transformers), but the high side version are quite a bit more expensive.

The details required to make the compensation are listed on the transformer nameplate, and the metering will be quite accurate. A metering engineer, a qualified meter technician and the meter-man's handbook will be required, but they easily pay for themselves.

Regards, CJM

__________________
I do not 'know it all', but i will admit that I would like to. CJM
Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#4

Re: KWH Reading Difference

06/23/2009 7:43 AM

there is something interesting about transformers. If you see the efficiency curves, the peak is somewhat abot at 50% load (and not 100%)

Then the efficiency slowly tapers off till 100% (and sharply on the 0% side)

This is about your second portion

The first portion is already answered- the secondary side power reading will be load power, assuming the transfromer efficiency appox 98-99% you may get the primary side power.

http://nptel.iitm.ac.in/courses/IIT-MADRAS/Electrical_Machines_I/pdfs/1_10.pdf

http://www.bicronusa.com/tpt_efficiency.html

The most probable reasson being that these are not supposed to work at full load (since for most - especially the distribution ones) the load is much lower that the full load value.

Just to give you an example- in my shed we have one 1MVA sub-station - a few days back I was surprised to find that the connected load (machines) is 1.5 MVA approx

However as we know that the machines do not run at full load eg a VTL drive motor of 75KW will rarely draw this power, and then all the machines at full load will not synchronise.

WSimilarly, all the domestic loads do not.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Reply
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#5
In reply to #4

Re: KWH Reading Difference

06/23/2009 8:03 AM

My bad - I was looking at ferroresonant transformers:

[Source]

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#6
In reply to #5

Re: KWH Reading Difference

06/23/2009 9:33 AM

Yes on Ferro resonant transformers you are correct.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Reply
Power-User
United States - Member - New Member

Join Date: Aug 2008
Location: KY, USA
Posts: 367
Good Answers: 18
#7
In reply to #5

Re: KWH Reading Difference

06/24/2009 12:09 PM

I think this is what you meant to show:

This is a good graph; it breaks out iron and copper losses then adds them together to make the "total loss" curve. It also shows peak efficiency at around 75-80% (which is what I have always been told working in the trade). Here's a link if you want to buy the book:

http://books.google.com/books?id=yKMJAAAAIAAJ&pg=PA309&lpg=PA309&dq=transformer+efficiency+curves&source=bl&ots=m4DF1f_ulf&sig=C4-Aa4Uurb8vxSaXSTefJfTnk88&hl=en&ei=fUhCSt_ALc3ktgeE6L2ZCQ&sa=X&oi=book_result&ct=result&resnum=10

Anyway, the efficiency of a transformer is very good, but it is not perfect, so it is most accurate to meter on the primary side of the transformer. However, if this is not practical, then metering on the secondary side will yield a value that is close to actual power used - provided that the transformer is not severely "under-loaded."

If you have a continuous load on the transformer, then it would not be unreasonable to treat the power loss in the transformer as a constant.

The efficiency rating of the transformer should be provided by the manufacturer. In the US it would be found on the nameplate of the transformer - it is usually abbreviated eff.

Use the eff rating to estimate "total loss" (which should be ~1-5%) by subtracting from 100%:

100% - eff = "total loss"

__________________
The most valuable of all talents is that of never using two words when one will do. ~Thomas Jefferson
Reply
Reply to Forum Thread 7 comments