If i will use 3 phase 4-pole ELCB in unbalance single phase load, will it trip? How about if using only L1, L2 & N (L3 is open)?
Re: 3 phase ELCB with unbalance single phase load.
06/24/2009 3:15 AM
No, it won't.
Re: Three-Phase ELCB with Unbalances Single-Phase Load
06/24/2009 8:42 PM
ELCB is called Earth Leakage Circuit Breaker. The ELCB will only trip if there is any current leakage to the earth. As long as your unbalance load of the 3 phase + the neutral wire with the total sum of "Zero" current (R+Y+B+N=0) then the ELCB will not trip.
Any current that leak to the earth (R+Y+B+N = < 0Amp), the ELCB will trip.
06/26/2009 10:13 AM
Thanks!