Maximum Demand Calculation

06/24/2009 7:13 AM

I got a problem. I am not an electrical engineer. I need to calculate the max demand for aproposed project. the data I have is 800 flats with each having an avg of 1000 Watts power requirement. now how do i do this?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Commentator

Join Date: Nov 2008
Location: S.E. Asia
Posts: 91
Good Answers: 1
#1

Re: Max Demand Calculation

06/24/2009 10:17 AM

Without being rude, 1000 watts is nothing. I live in Thailand (I'm Australian) & even the poorest of Thais have a minimum 15 amp (at 220 volts) supply. Where did you get this figure of 1000 watts per unit? Has future expansion been allowed for? Where are you?

__________________
"If you try to keep a leg each side of a barbed-wire fence, you'll do yourself a mischief." - Joh Bjelke-Petersen.
Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#2
In reply to #1

Re: Max Demand Calculation

06/24/2009 12:36 PM

It is 1000W average power I feel is perfectly Ok (in fact for me it is quite high) - 24 Units/ day or 720 Units/month for a normal domestic is high.

Let us say (my case) -1.5T AC - 7 Hrs - 7-8 Units,+ fridge, CFL lamps(negligible), fans etc- may not add up the other 10 Units.

But the max demand is other case -

1.5KW (AC) + may be my washing M/C is On (1.5KW) + M/W Oven+ All fans+ Tv+Fridge+ Electric iron+...

max demand may be about 7 to 8KW

So it is very difficult to predict the max demand from the avge unless you have any idea of connected loads.

BTW- there are moments when most of the loads are on simultaneously (I have observed it) except of course the lesser ones (fans and lights)

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Register to Reply
Anonymous Poster
#6
In reply to #2

Re: Max Demand Calculation

06/25/2009 10:56 AM

Please look at this calculation from a different direction. Using an average is not the correct approach. For example, if I have an air conditioner that runs in the evening and a refrigerator that cycles on and lights and a TV or stereo then the demand in the evening could be quite high. Now if I turn everything off and while I sleep and only the refrigerator cycles on and off during the night, the demand is low. If I average the two conditions and use this calculation for feeders and branch circuits, the installation will not be adequate. A better approach is to total the loads that will operate at the same time multiplied by 100% and add 125% of the largest load (probably the air conditioner). This will provide an adequate design without any room for future expansion. Take this figure and round-up to next highest common overcurrent device rating. Better to have more than enough than not enough. A design that is not adequate will be seen as a failure. Err on the side of caution.

Register to Reply
Guru
Panama - Member - New Member Hobbies - CNC - New Member Engineering Fields - Marine Engineering - New Member Engineering Fields - Retired Engineers / Mentors - New Member

Join Date: Dec 2006
Location: Panama
Posts: 4273
Good Answers: 213
#3

Re: Maximum Demand Calculation

06/25/2009 1:20 AM

Peak and average are going to have very little to do with each other. Are the flats occupied during the hot hours, or are most of the occupants at work then? Furthermore, power consumption is going to vary according to the season- even in the tropics, when the only seasons are "wet" and "dry", there will be significant variation in peak demand during the different seasons. How many residents in each flat? This will have an impact. What economic level are we talking about? Rich people use more power than poor people.

Forget the average. Calculate the load from each unit for all possible equipment- AC's, water heaters, refrigerators, lights, entertainment, computers, etc. Multiply that times 800. That is your peak load. The average has nothing to do with this.

Register to Reply
Anonymous Poster
#4

Re: Maximum Demand Calculation

06/25/2009 3:59 AM

Hi Sunnylele,

How do you arrive at this figure i.e 1000watts? Mind you load demand calculation is not just suming up the total power requirements of your appliances. Other factors like demand factors, diversity factors, load characteristics, and others are considered in accordance with IEE regulations.

I suggest you get an engineer to handle that for you, He will duly consider all necessary parameters to give the right estimate.

Register to Reply Score 1 for Good Answer
Participant

Join Date: Jun 2009
Posts: 2
#5

Re: Maximum Demand Calculation

06/25/2009 7:41 AM

thanks guys, your inputs helped solve my prob

Register to Reply
Commentator

Join Date: Sep 2008
Posts: 70
#7

Re: Maximum Demand Calculation

06/25/2009 8:27 PM

Just don't forget to check local codes when using diversity factor. Some local authorities don't like using diversities.

Register to Reply
Register to Reply 7 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); cwarner7_11 (1); elkangorito (1); ericpolc (1); sb (1); sunnylele (1)

Previous in Forum: Short Circuit Calculation   Next in Forum: Grounding and Earthing
You might be interested in: Optical Flats, Power Quality Analyzers, Mirror Mounts

Advertisement