Will It Hurt My PLC?

06/26/2009 1:41 AM

I am using 5 kva ups for my plc and associated system.Theorotically potential between earh and nuetral at o/p of ups recommanded to keep zero.My ups gives 21 volts. on backup mode (mains faluer)at o/p.This never lights bulb of 40 watt.

will it harm to my plc system.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: what shoud be nuetral earth potential for ups on backup.

06/26/2009 3:12 AM

No, it won't. Earth conductors are there to provide personnel protection to extraneous metal parts so that, in the event of a fault within the equipment that risks making the metalwork live, the circuit protective device will operate. There should not be, under normal operation, any connection between the phase and neutral conductors and earth within the appliance.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Aug 2006
Posts: 183
Good Answers: 2
#2

Re: Will It Hurt My PLC?

06/27/2009 1:33 AM

21 V earth to neutral voltage is VERY HIGH. Pls. check the earthing cable and neutral wiring. There is clear indication of problems likely to come up, including damage to your connected equipment also.

Thanks and regards

Ashok Toshniwal, Bangalore, India

Register to Reply
Commentator
Australia - Member - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Jan 2008
Location: Mount Gambier, South Australia
Posts: 56
#3

Re: Will It Hurt My PLC?

06/27/2009 3:39 AM

Hi,

I would check out the UPS details, sounds like the inverter maybe be a floating design. The PLC and other equipment wont have a problem if the inverter is maintaining a 'clean' voltage. The power supply in the PLC generally have good tolerances and output nice filtered voltage to the PLC components.

With the 40 watt lamp, were you able to measure any current, and did the voltage difference remain at 21V?

Regards

Trevor.

__________________
tooz
Register to Reply
Guru
Popular Science - Cosmology - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Energy Engineering - New Member Engineering Fields - Electrical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Electromechanical Engineering - Old Member, New Association

Join Date: Apr 2008
Location: Lexington, KY
Posts: 1639
Good Answers: 73
#4

Re: Will It Hurt My PLC?

06/27/2009 11:54 AM

First, your PLC and most other electronic devices run on DC power. So the synthetic AC power output from your UPS feeds the AC input of the DC power supply that the PLC uses.

Second, most UPS devices do not output a sinusoidal voltage. The output may look more like a square wave than a sine wave, but if your DC power supply is designed well enough, then everything should be OK.

Third, a voltage of more than 3 or 4 volts between neutral and earth ground indicates the possible presence of harmonic distortion. That comes from the non-sinusoidal output. You can place ferrite beads on your power line to reduce the higher frequency components of your simulated AC power from the UPS. But the potential to cause problems with the PLC depends on how well the DC power supply handles harmonic distortion. Since it probably has a step-down transformer, you should be sufficiently safe. It will either work, or it will be very confused and act strangely.

__________________
A great troubleshooting tip...."When you eliminate the impossible, whatever remains, however improbable, must be the truth." Sir Arthur Conan Doyle
Register to Reply
Anonymous Poster
#5

Re: Will It Hurt My PLC?

06/28/2009 12:02 PM

What do you mean by "o/p"?

Register to Reply
Power-User

Join Date: Aug 2006
Posts: 183
Good Answers: 2
#7
In reply to #5

Re: Will It Hurt My PLC?

06/29/2009 4:33 AM

Output

Register to Reply
Anonymous Poster
#6

Re: Will It Hurt My PLC?

06/29/2009 1:25 AM

Hi gentelmens, thanks for your reply .There is no current flow when iam connecting load to 21v between earth and nutral.

Register to Reply
Power-User

Join Date: Aug 2006
Posts: 183
Good Answers: 2
#8
In reply to #6

Re: Will It Hurt My PLC?

06/29/2009 4:35 AM

Current flow will depend on the resistance connected between earth and neutral. DO NOT SHORT EARTH & NEUTRAL, YOU MIGHT SEE SPARK OR EVEN EXPLOSION.