the problem of connecting two 750kva tranformers in parallel .

06/27/2009 8:32 AM

we intend connecting two 750kva transformers in parallel on the lv side, having two different vector group, one is dyn 11 the other is dyn5.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#1

Re: the problem of connecting two 750kva tranformers in parallel .

06/27/2009 9:42 AM

Please consult an expert (it is unlilely that you have done)

You are likely to be left with no transformers.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2
In reply to #1

Re: the problem of connecting two 750kva tranformers in parallel .

06/27/2009 11:19 AM

You can search the forum for more information. here is one answer:

http://cr4.globalspec.com/thread/4934/Types-of-Vector-Groups-for-Transformers

Reply
Guru

Join Date: Jul 2008
Location: SoCal USA
Posts: 556
Good Answers: 23
#3

Re: the problem of connecting two 750kva tranformers in parallel .

06/27/2009 2:59 PM
__________________
I do not 'know it all', but i will admit that I would like to. CJM
Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#4
In reply to #3

Re: the problem of connecting two 750kva tranformers in parallel .

06/28/2009 10:35 AM

In Dyn11, the phase angle of the LV winding lags the HV by 11x30 = 330 degrees with the corresponding phase (or leads 30 degrees); while in Dyn5, the phase angle of the LV winding lags the HV by 5x30 = 150 degrees with the corresponding phase or lags 150-120 = 30 degrees with another phase. In no case, you can connect it with having 0 phase difference in secondary side. So, it is not possible at all.

-MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply
Reply to Forum Thread 4 comments
Copy to Clipboard

Users who posted comments:

CJMcGill (1); msamad (1); sb (1); wareagle (1)

Previous in Forum: ABB Fully automatic star delta starter VS Siemens ditto   Next in Forum: electrical engineering softwares

Advertisement