Sizing DC Cables

07/03/2009 12:19 AM

Suppose I have a cable with the following details:

Size: 0.5mm^2

DC resistance: 3.84ohms/100m

Maximum Rated Current: 3A

Nominal Voltage: 150VDC

Suppose I wish to install this cable in an installation where the nominal voltage is 24V DC being protected by a circuit breaker of 6A. Is this OK, i.e. under short circuit or overload, will the breaker trip before the cable burns?

My thought is that it is ok. Since we are mostly concerned with the temperature of the cable (ignore volt drop for the moment), we consider the power loss accros the cable. For the nominal case, Pmax = Vnom x Imax = 150 x 3 = 450W

For the proposed installation, we have P = Vnom x Imax = 24 x 6 = 144W.

Using this reasoning, can we se that at 24VDC, this cable can carry:

P/V = 450/24 = 18.75A

Seems a bit large for a 0.5mm2 cable.

Any thoughts?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: DC cable sizing

07/03/2009 12:31 AM

Short answer - No, the cable is too small for the load current. Always size the cable for both the load current and the volt drop.

Best to use cable and a circuit breaker sized for the load.

__________________
jack of all trades
Reply
Anonymous Poster
#2
In reply to #1

Re: DC cable sizing

07/03/2009 1:04 AM

But surely all we need to worry about is the power dissipation of the cable. If the cable can disspate 450W @ 150VDC, then surely it can dissipate 450W @ 24VDC.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #2

Re: DC cable sizing

07/03/2009 3:17 AM

CR4 doesn't do arguments.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#10
In reply to #2

Re: DC cable sizing

07/03/2009 4:17 AM

Ah the point is that the cable cannot dissipate 450W, that is why I didn't bother mentioning the supply voltage (it isn't relevant to this particular question) only the current and volt drop across the cable. Also the load is 450W, not the power dissipated across the cable due to its resistance.

__________________
jack of all trades
Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#3

Re: DC cable sizing

07/03/2009 2:37 AM

Why

I = P/V = 450/24 = 18.75A

Are you planning to short circuit the cable?

I = 3A whatever may be the voltage and the loss is I2R irrespective of the voltage.

The P is the Load + loss power and not the one dissipated in the cable.

Hence the breaker must be rated for the 3A only.

All these calculations are complicating the issue.

The cable is of course not dissipating 450W - it is carrying 450W

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Reply Score 1 for Good Answer
Anonymous Poster
#4

Re: DC cable sizing

07/03/2009 2:54 AM

Ok, so confusiuon in terminology. To clarify the load is for example 6A @ 24VDC, which the cable must be able to carry: 6 x 24 = 144W. For say 100m of cable, the power dissipated by the cable is I^2R = 36 x 3.84 = 138.24W thus total power the cable must carry is 282.24W. For the maximum ratings the cable can carry 450W. Since the load + loss is less than the maximum, this should be ok? (this is all just hypothetical, just trying to get my thoughts straight). Ignore the voltage drop for now, assume an ideal voltage source.

Reply
Guru

Join Date: Mar 2007
Location: City of Light
Posts: 3943
Good Answers: 183
#5

Re: DC cable sizing

07/03/2009 3:05 AM

The capability to dissipate power of the cable is limited by the rated current : I^2*R in W/length. In your case 3^2*3.84/100= 0.3456 W/m!

The maximal voltage it can accept is limited by the insulation it self (max 150V).

So that in fact the cable can transport a power of 450 W for the "user" but can only dissipate ≈0.35 W/m!

AS you see two different aspects NOT related to each other in the way you assume.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: DC cable sizing

07/03/2009 3:41 AM

What on earth is the point of short-circuiting the supply voltage with a piece of cable? Cables are there to transfer energy from some place to some other place, not to act as room heaters!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#8

Re: DC cable sizing

07/03/2009 3:54 AM

So, voltage is unimportant in the current carrying capacity of a conductor, we could essentially put 11kV on this conductor, assuming the insulation was rated for 11kV and it would still carry 3A?

If the rated current is 3A and resitance is 3.84ohms/100m we have 0.35W/m. This is the rated power of the cable. If we were to run 6A through this cable we would have

36 X (3.84/100) = 1.38W/m, approximately 4 times the maximum allowable power, and the reason it is 4 times as it is a squared relationship ie (6A/3A)^2.

So, when the manufacturer says 'the current carrying capacity of this conductor is xxxA' this is the maximum allowable current regardless of the voltage applied (assuming an ideal installation method etc.)

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9
In reply to #8

Re: DC cable sizing

07/03/2009 4:08 AM

Well done.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Mar 2007
Location: City of Light
Posts: 3943
Good Answers: 183
#11
In reply to #8

Re: DC cable sizing

07/03/2009 5:36 AM

"This is the rated power of the cable."

NOT, it is only the power dissipation rate which depends on the heat transfer through the insulation and the way the cable can transfer heat to the ambient.

The dissipation is not the same for a cable in free air, in water or in the wall thus the maximal allowed current will not be the same.

In fact the current is limited by the acceptable losses as well. The resistivity increases with temperature so that if a cable runs hot the voltage drop will increase as well.

Those are the limitations: functional and economical.

For very short times the maximal current can be a lot higher as long as the maximal temperature, considering the cable and insulation accumulating capability and the thermal diffusivity of the insulation, do not go so high that the insulation molecular structure will be harmed.

If one looks at the current limits for different cables it is possible to determine the transfer coefficient of heat for the usual conditions which is between 2 and 4 w/m^2°K. Values based on external cable diameter.

Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#12
In reply to #8

Re: DC cable sizing

07/03/2009 5:53 AM

So, when the manufacturer says 'the current carrying capacity of this conductor is xxxA' this is the maximum allowable current regardless of the voltage applied (assuming an ideal installation method etc.)

Since it is entering the theoritical area.

1. remember AC and DC will have different capacity - Due to skin effect.

2. There will be effect of voltage due to the lekage losses. Though not in the practical area where you are going to work with limited voltages, but of course it will be prominent when, as you said at 11KV that is even if the insulation can withstand.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches
Reply
Reply to Forum Thread 12 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (3); jack of all trades (2); nick name (2); PWSlack (3); sb (2)

Previous in Forum: Trickle Charging and Batteries   Next in Forum: Supply Voltage in India
You might be interested in: Cable Laying Services, Cable Assemblies, Cable Trays

Advertisement