can high voltage transformer ie 11 kv / 132 KV 63 MVA be energise from primary side ie from 11 kv side while 132 kv side breaker is closed on dead bus .On primary side 11 KV is coming from diesel engine of 15 MW rating. at the time of energising transformer the out put of engine is about 1 MW.We can not put load on the generator bcz we dont have load to put on the generator .
Re: ziazia
07/05/2009 6:27 PM
" ... 132 kv side breaker is closed on dead bus ... "
Do you mean open circuit (no load)?
Re: ziazia
07/06/2009 5:24 PM
132 kv side breaker closed on dead bus and bus is not connected to any load .
after starting DG dg breaker closed also on dead bus from that bus auix transformer 3.15 kva energise to give auix voltage ie 440 V to our engine auxilaries.Now we like to close transformer 11 KV side breaker to energise 132 kv transformer on NO-load ...on dead bus later from that bus after getting voltage we will supply load to utility ( small load about 12 MW slowly ) hope i understad .
Re: ziazia
07/06/2009 5:30 PM
ya at no load
Re: ziazia
08/12/2012 4:21 AM
yes.
Re: Can a high voltage transformer be energized from the primary side?
07/05/2009 6:35 PM
YES
Good Answers: 244
07/05/2009 10:04 PM
"at the time of energising transformer the out put of engine is about 1 MW" - what are the 1 MW loads. Does the generator supplying load through other transformer?
I wouldn't answer it by simply "YES". There are few things to consider:
1. If the transmission line is too long, then the generator can experience a high capacitive load of leading power factor and it may cause the generator voltage regulation system unstable. Synchronous generators are unstable while supplying leading power factor loads. In your case, the generator seems supplying 1 MW load. If resultant power factor of the current 1 MW load and the transmission line capacitive load is lagging (I am guessing so), then it should be OK.
2. Before energizing the transformer, make sure there is appropriate protection enabled for the generator, transformer and 132 KV transmission line.
3. This is not a suggested method. For safe operation, energize the transformer first (keeping the 132 KV side breaker open), then close the 132 KV breaker. However, it doesn't prevent you to do the way you described.
-MS
07/06/2009 5:32 PM
1 MW only station load
Good Answers: 103
07/05/2009 9:58 PM
There may not be a problem of charging the transformer. But assuming you are on a grid, how do you synchronise when later the HV breaker is closed?
When you don't have load on the generator why do you want to run it at all ? it will just feed the no load current of the transformer. DGs are quick start so when the load is available, start it.
07/06/2009 5:36 PM
breaker is closed on dead bus having 0 volt.
Australia - Member - New Member Hobbies - Target Shooting - New Member Popular Science - Weaponology - New Member
07/05/2009 11:24 PM
This sounds like a scary scenario to me.
Regardless of is it possible, I would think that is Must Not be done for safety reasons.
Transformers are not generally direction sensitive, just step-up or step-down.
If the Primary side breaker is closed you would be backfeeding to the grid, which is putting the unsuspecting lines workers at risk as the line they thought was dead is now live.
Also if the circuit becomes live from the supply end and the generator and mains are out of sync...Well then it is really all about the Boom cause something is goning to give.
I would have thought that the breakers on the Main Switch Board for the incoming Mains and the Generator would be Mechanically interlocked to ensure that they can not both be closed at the same time.
Regards,
Sapper
It's all about the Boom! - MythBusters
07/06/2009 5:40 PM
like to give voltage on dead bus which is in our switch yard and no feeder is connected to that bus bcz all feeder breaker was in open condition.
08/12/2012 4:29 AM
Actually I am talking about back feeding .when utility company asked me at the time of city black out to supply back feed at least on important feeder whose load is less then the generator out put.