Earthing instrument body

07/06/2009 1:27 PM

Dear Experts,

My Instrumetns are installed on a skid. The skid itself is earthed from two different points. The instrument is hooked up using a single pair instrument cable with a shield. However, the instrument body is not earthed. My question is that, is it necessary to separately earth the instrument body? Please reply by referring relevant IEC or equivalent standard.

Regards,

Naseem QAMAR

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: Earthing instrument body

07/06/2009 4:44 PM

Please reply by referring relevant IEC or equivalent standard

That's funny I was going to tell you the same thing, it is interesting that you don't seem to know what the relevant standards are (are you an electrical consultant?).

Do the instruments require earthing? Are they designed to be earthed? Does the manual tell you to earth them?

If the answer is yes to any of the above questions then you need to earth the instruments for safety and/or correct instrument functionality.

If in doubt read the standards (or at the very least the instrument manual).

__________________
jack of all trades
Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Earthing instrument body

07/07/2009 3:24 AM

It is good practice to earth it, necessary or not.

If the output is a current signal, earthing it should make no difference to its performance.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster
#3

Re: Earthing instrument body

07/07/2009 11:00 PM

If you are talking about the single pair cable shield it should be only connected at one end so that you dont get any eddy currents within the loop

Reply
Associate

Join Date: Jun 2008
Location: Houston
Posts: 30
#4
In reply to #3

Re: Earthing instrument body

07/14/2009 11:02 AM

Depending on the installation method the device is sometimes grounded to the piping or to the conduit if that method of installation is used. This connection is only a mechanical ground not that of the wiring as indicated in the comment above which as indicated prevents ground loops in the system.

Reply
Active Contributor

Join Date: Jul 2009
Location: Western Australia
Posts: 24
#5

Re: Earthing instrument body

07/22/2009 12:39 AM

Site standards may specify the bonding of all elctrical apparatus, but regulatory standards usually do not.

The main purpose of bonding the instrument body is for hazardous area applications to reduce ignition source potential from induced or fault potentials.

If it is in a hazardous area, get a hazardous area consultant to assess the installation.