Wire Sizing and FLA and LRA Motor Ratings

07/06/2009 9:36 PM

In sizing the wire for power supply, also for breaker, what we will use the FLA or RLA rating of the motors?

__________________
Imagination is better than knowledge for knowledge is limited while imagination embraces the entire world and give birth to development and success.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: FLA or LRA? (motors nameplate)

07/06/2009 9:57 PM

FLA in the USA. Don't know where you are.

Register to Reply
Participant

Join Date: Jul 2009
Posts: 3
#2
In reply to #1

Re: FLA or LRA? (motors nameplate)

07/06/2009 10:18 PM

Thank you for the info.

__________________
Imagination is better than knowledge for knowledge is limited while imagination embraces the entire world and give birth to development and success.
Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#3

Re: FLA or LRA? (motors nameplate)

07/07/2009 12:18 AM

For sizing wire for the motor will be FLA + other factors like, the distance, Ambient temperature factors, fault level and your motor starting amps.

Sizing for the main breakers will be slightly different.

Sizing for the cable. (Example 1)

For example,

if you have a motor rated at 1KW with voltage at 415V and PF at 0.85 and your motor FLA is 1.636 Amp, then,

The cable size will be (as per in the cable data sheet) will be 1 mm2 but in generally, we will use 2.5 mm2. ( I don't know why we always use 2.5 mm2 cables)

Sizing for the Breaker (MCB)

Since your motor FLA is 1.636 Amp. The MCB will be 6 Amp MCB. (I think the 6 Amp MCB look better than the 2 Amp MCB)

Sizing for the cable (Example 2)

For example,

If you have a motor rated at 185KW with voltage at 415V and PF at 0.85 and your motor FLA is 302.83 Amp, then,

The cable size will be (as per in the cable data sheet) will be 185mm2. But in generally, we will use 240 mm2 by giving some allowance of 16% extra capacity for the starting motor current and the faults level of the motor. (in case the motor short circuited, at lease the cable still able to withstand the faults current until the Main MCCB trip Off.)

Sizing for the Breaker (MCB)

Since your motor FLA is 302.83 Amp. The MCB will be 600 Amp MCCB. Why, don't forget your motor starting current. (this is for motor with soft starter system)

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: FLA or LRA? (motors nameplate)

07/07/2009 3:13 AM

Full load current. The locked rotor current should only be there for as long as the circuit protective device takes to operate.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Jun 2009
Posts: 2
#5

Re: Wire Sizing and FLA and LRA Motor Ratings

07/08/2009 12:08 AM

I believe FLA criteria will take care!

Register to Reply
Anonymous Poster
#6
In reply to #5

Re: Wire Sizing and FLA and LRA Motor Ratings

07/08/2009 5:52 AM

For conductors 1.23 of FLA and for breakers, it will depend on the Code Letter for use of the LRA to determine breaker. Likewise, consider type of controller for use of LRA.

Register to Reply
Active Contributor

Join Date: May 2009
Location: Western PA, US
Posts: 22
#7

Re: Wire Sizing and FLA and LRA Motor Ratings

07/08/2009 6:13 AM

In the US your wire sizing is, according to the NEC, 125% of FLA. The starter, breakers aren't sufficient for motor duty, must have 25% headroom but can be adjusted to match the FLA of the motor.

__________________
Very funny Scotty, now beam down my clothes!
Register to Reply
Power-User

Join Date: May 2008
Location: San Jose, CA, USA
Posts: 121
Good Answers: 2
#8

Re: Wire Sizing and FLA and LRA Motor Ratings

07/08/2009 12:44 PM

When sizing the power supply wires, consider the full load current (FLA, full load amperes, In, rated current, nominal current) x 1.25 to account for additional heat generated during the starting process. This is valid for motors with continuous duty. Feeders for motors with heavier duty factor ( frequent starts, reversing, etc) have to be larger, considering the higher starting current occuring more often over the same period of time.

Since the starting process duration is also dependent on the voltage at the motor terminals, the wire size selection should also consider voltage drop during the starting period, especially for excessive feeder lengths.

The LRA (locked rotor amperes, short circuit current, locked rotor current) is dependent on the design type of the motor and is not to be considered in sizing the feeder under normal circumstances. If it would, the feeders would be way oversized.

Sizing the overcurrent protection (thermal-magnetic breaker) is (for general use motors) with breaker trip setting between 300% and 150% of the full load current ( the higher % for lower ratings; this is not intentional but due to the fact that the breakers are manufactured with standardized trip values ( as an example for the US) minimum rating of a general use circuit breaker is 15A and the current for a 1 HP, 208V, 3-phase motor is 4.8A, resulting 312% , for 2 HP (7.8A) it would be 192%, for 75 HP (221A) with a breaker rated 300A it would be 135%) Setting a too low value leads to nuisance tripping during start, a too high value defies the role of a protection device.

__________________
Scientes et audaces fortuna juvat !
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#9

Re: Wire Sizing and FLA and LRA Motor Ratings

06/16/2023 9:36 AM

There are procedures that cover this matter in national electrical standards, such as British Standard 7671, for example.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); lyn (1); op_borz (1); PWSlack (2); rstanley3105 (1); shirodkara (1); Simon Wan (1); tomad (1)

Previous in Forum: Backup Batteries for Stations and Sub-Stations   Next in Forum: Cable Rating of Data Center

Advertisement