Anonymous Poster

Grounded Neutral

07/07/2009 9:22 AM

I have run in to another instance of the electricial person grounding the neutral to the ground bar and ground rod in a MDB.

This is causing a lot of voltage problems.

When is it ever acceptiable to ground the neutral in a residential MDB?

Thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Grounded Neutral

07/07/2009 9:24 AM

When the system earthing scheme requires it. Check out the Wikipedia article on earthing systems for more information.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User

Join Date: Dec 2006
Posts: 346
Good Answers: 6
#2

Re: Grounded Neutral

07/07/2009 9:59 AM

guest; in the USA the NEC requires the main service neutral to be grounded to ground rods, or copper underground water supply. perry

Reply
Power-User
United States - Member - New Member

Join Date: Aug 2008
Location: KY, USA
Posts: 367
Good Answers: 18
#3

Re: Grounded Neutral

07/07/2009 10:48 AM

In the US, as a general rule, the primary side first electrical disconnecting means after a transformer (or electrical source) should have its neutral bonded to ground. In a distribution panel this is usually accomplished by driving a green hex-head screw through the neutral bar and into the case of the panel. This can also be accomplished by installing a properly sized conductor between the neutral and ground bars.

Note: In some parts of the US the neutral-earth bond is required to be done in the meter base. If the neutral is bonded in the meter base, then it must not be bonded again in the panel or disconnect.

Electrical sub-panels (panels fed from another panel or disconnect rather than from a primary source) should not be bonded to ground. So if an off-the-shelf distribution panel is to be used as a sub-panel , then the green bonding screw is not supposed to be installed, and the neutral bar must be insulated from the housing of the electrical enclosure.

Here's a good website for more information:

http://ecmweb.com/nec/code_top50nec_092506/

__________________
The most valuable of all talents is that of never using two words when one will do. ~Thomas Jefferson
Reply
Active Contributor

Join Date: Jun 2008
Posts: 11
#4
In reply to #3

Re: Grounded Neutral

07/07/2009 5:00 PM

Hi,

The electrical guy connected the ire from the ground rod to the ground bar and a jumper to the neutral bar. Here the power company often looses the neutral. won't the system use the ground as the neutral if the neutral is missing?

Thanks

Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#6
In reply to #4

Re: Grounded Neutral

07/08/2009 12:03 AM

Yes...

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply
Power-User
United States - Member - New Member

Join Date: Aug 2008
Location: KY, USA
Posts: 367
Good Answers: 18
#7
In reply to #4

Re: Grounded Neutral

07/08/2009 8:55 AM

A simple Google search for "neutral bonding jumper" will produce over 17,000 websites that will give lots of good reasons for bonding the neutral.

__________________
The most valuable of all talents is that of never using two words when one will do. ~Thomas Jefferson
Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#5

Re: Grounded Neutral

07/07/2009 11:50 PM

In Canada... Required by code is the following.

  • The consumer service "neutral conductor", the "identified conductor", must terminate in the service entrance equipment on the "neutral bar".
  • A "grounding conductor" must then connect the neutral bar to a "grounding electrode".
  • A "bonding jumper" connects the neutral bar to the service raceway via a grounding bushing.
  • A "bonding conductor" then connects neutral bar to the case of the service equipment. This is the starting point of the "bonding system".

The section of the CEC that contains these requirements is Section 10.

Here is a diagram.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply Score 1 for Good Answer
Power-User
United States - Member - New Member

Join Date: Aug 2008
Location: KY, USA
Posts: 367
Good Answers: 18
#8
In reply to #5

Re: Grounded Neutral

07/08/2009 9:36 AM

Thanks No60,

I'm pretty sure that we have said the same thing, though your post is better illustrated.

Do they not use the "green screw" in Canada? (This would only be provided if the distribution panel has a main breaker in it.)

__________________
The most valuable of all talents is that of never using two words when one will do. ~Thomas Jefferson
Reply Off Topic (Score 5)
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#9
In reply to #8

Re: Grounded Neutral

07/08/2009 10:39 PM

Hey there EE...

Yes, we use green screws or straps or jumpers.

Glad you liked the drawing... though for some reason it posted fuzzy.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Reply Off Topic (Score 5)
Reply to Forum Thread 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

EElectrician (3); farang1 (1); North of 60 (3); perry (1); PWSlack (1)