Earthing in Substation

07/09/2009 3:18 AM

Can we do welding & repair to earthmat in any charged electrical Substation?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Earthing in Substation

07/09/2009 3:29 AM

Should an earth fault develop while the operation is taking place, it would place the operative(s) at risk of electric shock depending upon the integrity of the remainder of the system and whereabouts on it the repairs are taking place.

It would be far better to do the repairs while the substation were de-energised, on health & safety grounds.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Associate

Join Date: May 2009
Location: Kansas City, Missouri
Posts: 48
Good Answers: 2
#2

Re: Earthing in Substation

07/09/2009 6:24 PM

Safety first.

__________________
E pur si muove -- Galileo
Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#3

Re: Earthing in Substation

07/09/2009 8:11 PM

Generally, basically, and normally, no welding & repair works to the earthmat is allowed in the substation while the substation is energize. It is dangerous to the workers and the equipment.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....