Phase Imbalance Problem - Welding Transformer

07/10/2009 1:40 AM

When we are using Two lines of Three phase(i.e 415 VAC each Phase) Welding Transformer on Power Generator then Phase will get imbalance. so how we can use this welding equipment on power generators.welding trasfomers is capable to delevered 400 out put current on 60% duty cycle.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Phase imbalance Problem - Welding Transformer

07/10/2009 3:22 AM

With one phase not connected the equipment behaves as though it is a single phase appliance at 415V. It's no problem in principle, provided the supply can handle it. And if it can't then expect a circuit protective device to operate, maintaining safety of the supply cabling.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Jul 2009
Posts: 7
#2
In reply to #1

Re: Phase imbalance Problem - Welding Transformer

07/10/2009 11:04 AM

It's Ok,

But during welding input current will flow only in two phase & one will be free, in this condition generator get loaded on two phase only & some times Generator trips,so what is solution to balance the load of three phases.

I don't know if I am not wrong we can connect three welding machines in this way that all phases should be loaded equaly.

i.e one will be between R & Y

Second will be Between Y & B

Third will be between R & B

What you say ??? is correct or not.

My mainn query is to balance the load of My Generator.

Register to Reply
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#5
In reply to #2

Re: Phase imbalance Problem - Welding Transformer

07/11/2009 10:34 AM

You are correct in principle but it is not likely that all the welding machine will operate simultaneously and at similar power. But if you have many, do distribute them on the three phases.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#3

Re: Phase Imbalance Problem - Welding Transformer

07/11/2009 1:26 AM

If your generator is large enough to handle 2 phase loading of your welder there should be no problem.

Fitting 3 welders to balance the phases wont work it will be worse because the total load will kill your generator if it cant handle a two phase load. in any case your welders will never be truly balanced as their individual loads are variable and intermittent.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Guru

Join Date: Mar 2007
Posts: 2550
Good Answers: 103
#4

Re: Phase Imbalance Problem - Welding Transformer

07/11/2009 9:44 AM

1. Why are you posting in this forum? assuming you are not student (are you?) you should have been in EE forum for more exposure. Of course if it is a part of education then this is OK.

2. The generators are typically able to take about 10% or so current in negative sequence (caused due to phase imbalance)

If your generator is large enough then it can probably accommodate the unbalance caused since the 400A at outlet will translate to only somewhere about 20A or so at inlet.

Also your generator is likely to be protected against the phase unbalance relays. Check them. However if you feel the unbalanced load/total load is high, use 3 phase welding generator/rectifier. Infact for our facility all are 3 phase only whether solid state or the old generator type.

__________________
Fantastic ideas for a Fantastic World, I make the illogical logical.They put me in cars,they put me in yer tv.They put me in stereos and those little radios you stick in your ears.They even put me in watches, they have teeny gremlins for your watches