Can I mount a gage PT above a liquid process tap.

07/10/2009 11:58 PM

Gents - I would greatly appreciate any input on this matter.

I plan on tapping a water distribution pump discharge manifold for a gage pressure transmitter. The pt will have a two-valve (vent & isolate) integral manifold. The pump discharge manifold is located outside and above grade. The manifold is low to the ground and limited space is available at the process tap location. It would be difficult to access the pt if located here especially since a heated enclosure would be required. There's a building located adjacent to the process tap and would provide an ideal location as there's plenty of room for access and it's a controlled environment. The finished floor of the building is approximately 3 ft above the centerline of the pump discharge manifold and the pt would be located 4.5 ft above the floor. There's room to make the process tap on either the side or bottom of the pipe. My questions are as follows:

1. If the pt is located in the building, will air in the impulse piping be a problem?

2. Does anyone have any suggestions?

3. Can anyone tell me where to find some typical details for a gage pt and impulse piping?

Thanks in advance for the help.

Register to Reply
Pathfinder Tags: gage pressure transmitter
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Commentator

Join Date: Apr 2009
Location: Texas
Posts: 57
Good Answers: 2
#1

Re: Can I mount a gage PT above a liquid process tap.

07/12/2009 7:20 AM

Ideally, you want the PT below the pipe. With the PT mounted 7.5 ft higher, keep the following in mind:

Slope any horizontal runs up toward the PT to aid in venting. Not sure offhand, but 1/8"/ft would not be unreasonable. (some may call this overkill)

Apply head correction to the PT calibration (zero output higher by 7.5 ft H2O)

Purge air out of the lines with the pump on.

Realize that if you have the slightest leak at the transmitter, you may lose your impulse piping fill, causing the PT to read higher than normal.

Realize that if the HC is insignificant compared to the range of the PT, then air in the impulse line will cause insignificant errors. And vice versa.

Good luck-

Register to Reply
Participant

Join Date: Jul 2009
Location: Alabama
Posts: 2
#2
In reply to #1

Re: Can I mount a gage PT above a liquid process tap.

07/12/2009 12:30 PM

mkruger21,

Thanks for the help.

Just to make sure I follow you, the PT range in this case is -14psi to 300psi, the expected system pressure fluctuation is 45psi to 110psi, and the HC (i'm still learning here so i assumed you were talking about head correction) would be 3.25psi(7.5 ft H2O).

So in this case, even if the impulse piping becomes filled with air, errors will be insignificant. Correct???

Thanks!

Register to Reply
Commentator

Join Date: Apr 2009
Location: Texas
Posts: 57
Good Answers: 2
#3
In reply to #2

Re: Can I mount a gage PT above a liquid process tap.

07/14/2009 8:48 AM

Your potential HC error is 3.25/314 = 1.04% full scale.

To me, that sounds insignificant based on the description of your system. If you correct for head, and your line stays full, then 1% saved is 1% earned.

Register to Reply
Active Contributor

Join Date: Jul 2009
Location: Western Australia
Posts: 24
#4
In reply to #1

Re: Can I mount a gage PT above a liquid process tap.

07/24/2009 12:30 AM

Beg to differ,

If the impulse piping has air ingress when the pump is off, it will leak the air back out soon enough when running again.

For your measurement range, not a problem.

Just make sure you compensate correctly (10 kPa/m, 0.435 psi/ft) and maintain a 1:10 slope.

Register to Reply
Commentator

Join Date: Apr 2009
Location: Texas
Posts: 57
Good Answers: 2
#5
In reply to #4

Re: Can I mount a gage PT above a liquid process tap.

07/24/2009 6:51 AM

Your point about the bidirectional leak is well taken. Thanks.

Register to Reply