and want to operate in SYCHRONZING , Please advise how to calucate for droop CT , AVR is R448 Leroy somer
The generator line current should be in the range of 1800 A. So, I would suggest you to select CT (one for each Genset) of
2000/1 A, 2.5 VA (or more), CL 1