IGBT Problem

07/15/2009 8:38 AM

DEAR FRIENDS;

am using igbt modules for motor speed control application.

To turn ON and OFF gate, i using pc923 ic for switching. +15,gnd and -5 voltage for

pc923 ic. It works fine, but rare case gate to collector is short.

what will be the reason?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#1

Re: IGBT Problem

07/16/2009 6:13 AM

Mr.Moorti,

The information is not enough. What are the values of biasing resisters of IGBT? What is the IGBT number? PC 923 gives max. 10mA. Is it ok to drive the IGBT? You motioned that IGBT stays turn "ON"; if that is correct you should decrease the values of biasing resistors that try to keep IGBT in "OFF" condition.

__________________
Subramanyam
Register to Reply
Associate
India - Member - moorthi

Join Date: Sep 2007
Posts: 26
#2
In reply to #1

Re: IGBT Problem

07/16/2009 8:14 AM

my doubt is, when collector to gate become a short in igbt module?

Register to Reply
2
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#3

Re: IGBT Problem

07/16/2009 10:05 AM

Back EMF is your likely problem. Your motor by definition is an inductive load. If you don't have a planned snubber like current path for when the IGBT turns OFF, the current will make a path one last time through the IGBT. Poof.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Jun 2005
Posts: 104
#4
In reply to #3

Re: IGBT Problem

07/17/2009 12:05 PM

I think you meant to ask if the original poster is using anti-parallel diodes with his modules. If not, obviously that will pose a problem with continuous-current conditions that require free-wheeling of said current.

Register to Reply
Power-User
Australia - Member - Igor...pull the switch!!!

Join Date: Apr 2009
Location: Australia, sunny North Queensland
Posts: 380
Good Answers: 12
#5
In reply to #3

Re: IGBT Problem

07/18/2009 3:28 AM

Agreed and good answer, assuming the OP's mentioned driver is suited for the unknown IGBT...I am surprised that the driver does not switch off the IGBT to prevent a potentially damaging short.

As mentioned by redfred, you need to solve for an inductive load, which is the motor(?) in your case. The spec sheet for your driver and/or IGBT should have a solution for this...without me even looking. Cheers.

__________________
CraziestOzzy
Register to Reply
Register to Reply 5 comments