Power Cable and Control Cable

07/16/2009 11:58 PM

I have placed a control cable in a conduct that contains a 415V power cable, I found that electrical interference due to the power cable (I guess) has affect the performance of the control cable, it create noice in the contral cable...

Is there any solution to reduce or minimize the electrical noise?

Thank you..

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Anonymous Poster
#1

Re: Power Cable and control cable

07/17/2009 12:38 AM

Separation, shielding, ensuring control cable signal & return are twisted and/or shielded. All these are standard techniques.

emc_c

Reply
Associate

Join Date: May 2009
Posts: 32
#2

Re: Power Cable and control cable

07/17/2009 3:39 AM

please give More details about your machine,about the power cable(is it from a VFD) and also the control cable supply voltage.

You can use copper shielded cables for reducing noise and shielding must be Earthed

Reply
Active Contributor

Join Date: Mar 2009
Location: TURKIYE
Posts: 11
#3
In reply to #2

Re: Power Cable and control cable

07/18/2009 2:28 AM

you should furnish control and electrical cable in seperate conduits. according to NEC,these cables has to be seperate.

__________________
electrical and electronic engineer
Reply Score 1 for Good Answer
Active Contributor

Join Date: May 2009
Location: Philippines
Posts: 23
#4

Re: Power Cable and Control Cable

07/18/2009 5:48 AM

The code does not allowed control and power cable of different systems to be mixed in the same conduit. Also, if cable of the same system is mixed in the same conduit, their voltage rating must be the same.

Regards.

Rudy C. Fernando

Reply
Active Contributor

Join Date: Jun 2009
Posts: 21
#5

Re: Power Cable and Control Cable

07/18/2009 1:50 PM

Close examination of install directions should reveal their recommendation to run a separate conduit for control cables due to eddy currents present around any electrical cable.These currents will produce unwanted inductive current in the control cable.It may cause the control to fail or act erratic.

Reply
Anonymous Poster
#6
In reply to #5

Re: Power Cable and Control Cable

07/18/2009 11:14 PM

When you will lay the Control & Power cable... use different tray for cables..keep a minimum 10mm distance between trays. Use Collective and individual screening control cable...

Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#7

Re: Power Cable and Control Cable

07/19/2009 3:22 AM

Firstly, I don't know what the regulations are where you live with regard to laying signal and power cables together, but do follow that as a first.

I personally do not see a problem with putting them together provided that they are well insulated from each other AND all the signals are each sent as differential twisted pairs (two wires per signal) over the cable. There is a need for some extra electronics at each end.

You may find that something like the DS96176, RS-485/RS-422 Differential Bus Transceiver, which you will find here, may supply a quick and effective method of implementing such electronics....

...but only if regulations allow of course......

Using differential drivers is always a good way of reducing the effects of interference on signals.....here is a reasonable explanation of how they work, I hope it helps you further.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Reply
Associate

Join Date: Aug 2008
Location: Nigeria, West Africa (+1 GMT)
Posts: 46
#8

Re: Power Cable and Control Cable

07/20/2009 9:44 AM

If you cant run seprate conduits for the power and control cables, then you should maintain atleast 10cm distance inbetween them.

__________________
One good Thing deserves Another
Reply
Reply to Forum Thread 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

akinbaglan (1); Andy Germany (1); Anonymous Poster (2); EnB (1); jaykrish (1); rudy_fernando5r (1); tonycaudill (1)