Transformer oil

07/18/2009 7:59 AM

Hey......I have met with a situation of topping up of transformer 11/0.433KV,2000KVA with oil of breakdown strength 27KV.Is it advisable?We normally do it if the breakdown strenght is more than 30KV.Is there any standards that approves it?

__________________
"Know something about everything and everything about something"
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Participant

Join Date: Jul 2009
Posts: 1
#1

Re: Transformer oil

07/19/2009 1:02 AM

good oil are medium voltage aparature 35 kv/2.5 mm high voltage aparature 50 kv/2.5 mm caution : characteristik of the oil for know oil conditions

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#2

Re: Transformer oil

07/19/2009 3:57 PM

There are transformer construction and maintenance standards that cover this. What country are you in (or what country's standards are the transformer built to) as they are country dependent.

__________________
jack of all trades
Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#4
In reply to #2

Re: Transformer oil

07/20/2009 1:02 PM

Thanx......I belong to India...its true that diffferent country follow different standars can u pls tell me is it recommended in your standard...?

__________________
"Know something about everything and everything about something"
Register to Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#3

Re: Transformer oil

07/19/2009 9:15 PM

In general, any transformer oil with breakdown dielectric strength of 27KV, which is much higher than acceptable level of 15KV is acceptable for the 11KV system. There is a standard that approves it but it depend upon the country by country.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Register to Reply
Power-User

Join Date: May 2009
Location: Some where on Earth !!!.
Posts: 243
Good Answers: 2
#5
In reply to #3

Re: Transformer oil

07/20/2009 1:03 PM

Thanx......I belong to India...its true that diffferent country follow different standars can u pls tell me is it recommended in your standard/country...?

__________________
"Know something about everything and everything about something"
Register to Reply
Register to Reply 5 comments
Copy to Clipboard

Users who posted comments:

giri (2); jack of all trades (1); raden-ngabehi (1); Simon Wan (1)

Previous in Forum: Earth cable   Next in Forum: QCS System Problem Honeywell Experion PKS

Advertisement