Dissolved Gas Analysis Results interpretation

07/19/2009 7:35 AM

Dear all,

We have 26.25 MVA , 220/11.5 KV transformer in our plant.

Bucholz alarm came on 28.06.09. We switched off the transformer and collected oil samples from the top valve, bottom valve and bocholz relay.

We conducted the DGA test on it and got these results :-

GASConcentration in ppm
H228
O2173831
N2593952
CH48
C2H44
C2H61
C2H22
C3H6+C3H81
CO2615
CO124

Can you please interpret these results for me, as to which of the faults is in developing stage by looking at those gas concentration levels ?

Is the level of C2H2 (2 ppm) normal as per the DGA test..?

If the transformer is normal then why bucholz relay alarm came..?

Your immediate comments are solicited.

Thanks.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: Dissolved Gas Analysis Results interpretation

07/19/2009 8:23 PM

Which stage alarmed?

What was analysis baseline?

Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#2

Re: Dissolved Gas Analysis Results interpretation

07/19/2009 8:24 PM

When your transformer trigger the bucholz relay, you have to shut down your transformer until future test has to be conducted. From your transformer oil results, your Hydrogen (H2) level with 28ppm is high not to mention your other gases, Oxygen with 173831 ppm and the Nitrogen 593952 ppm. What about the moisture content of your transformer oil?. I wouldn't find it in your table. With these O2 and H2 high level, I do belived that your moisture H2O is also very high ppm.

I suspected there is some faults in your transformer.

Please get a 2nd oil test sample again and you need to do some pressure and tan-delta test on your transformer to identified the faults on your transformer.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Commentator

Join Date: Jul 2009
Location: chennai, India
Posts: 55
Good Answers: 1
#3

Re: Dissolved Gas Analysis Results interpretation

07/20/2009 4:23 AM

Please see the chart

It gives the permissible Limits of Gas levels in relation to age of the transformer

In your Transformer non of the above limit is exceeded.

If Any thing Exceeded ,then we can go for analysis of fault.

Therfore your Tranformer is Healthy.

Please confirm whether the transformer is recently commissioned. In that case, there is every possibility that the trapped air in the winding and other areas During Hot Oil circulation, get released due normal vibration and collected at Bucholtz relay.

Dissolved key gas concentration limits in ppm

Status Hydrogen H

2

Methane

CH4

Acetylene

C2 H 2

Ethylene

C2 H 4

Ethane

C2 H6

Carbon monoxide

CO

Carbon dioxide

CO2

Normal 100 120 35 50 65 350 2500
Modest concern 101-700 121-400 36-250 51-100 66-100 351-570 2500-4000
Major Concern 701-1800 401-1000 51-80 101-200 101-150 571-1400 4001-10000
Imminent Risk >1800 >1000 >80 >200 >150 >1400 >10000
__________________
There is nothing either good or bad, only thinking make it so -
Reply
Anonymous Poster
#4

Re: Dissolved Gas Analysis Results interpretation

07/20/2009 9:06 AM

My main concern would be the C2H2 level. C2H2 is formed when oil sustains a temperature of 700degreesC, indicating a possible internal arcing.

Reply
Active Contributor

Join Date: Sep 2009
Posts: 12
#6
In reply to #4

Re: Dissolved Gas Analysis Results interpretation

02/12/2012 6:22 AM

Hi, Can you please tell me the limits of C2H2 levels prescribed for unused oil? Should it be 'Zero' in unused oil? Which IEC or other standard applicable for this?

We have results of 0.3 ppm in Transformer oil. The transformer is still not energised and just completed all Pre-commissioning tests. The oil is in the transformer for long 1.5 years.

Reply
Anonymous Poster
#5

Re: Dissolved Gas Analysis Results interpretation

07/20/2009 2:36 PM

hi..

No, The transformer is not recently commisioned. It has been in service for 4.5 years. and yes water content as per the testing authority was within the specified limits. i don't have the details now. But ya we inspected the JB of wires connecting bucholz relay to control and relay panel having RET521 relay and we found water ingress in it. Water was removed from the JB, and now the annunciation having "Transformer Trouble Alarm" has vanished. RET521 was showing intermittent alarm of Bucholz operated. Now, it is also not coming.

Can it was because of that..?

Thanks for the suggestions .

Reply
Active Contributor

Join Date: Sep 2012
Posts: 14
#7

Re: Dissolved Gas Analysis Results interpretation

09/12/2012 11:37 PM

how about if the carbon dioxide exceeds the limits ?