Temperature Controller Calibration

07/22/2009 1:40 PM

Is it necessary to calibrate temperature controller or is it because of different heater we are getting different reading for sealing temperature in verical form fill seal machine. Please guide.

__________________
thoughts becomes things.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
South Africa - Member -

Join Date: Nov 2008
Location: Johannesburg
Posts: 295
Good Answers: 12
#1

Re: Temperature Controller Calibration

07/23/2009 12:57 AM

Hi there,

If your temperature element is wired to the controller - the controller also has a transmitter circuit, so yes it would be necessary to calibrate it. For more information - refer to the controller documentation.

Regards,

Craig

Register to Reply
Guru
Philippines - Member - New Member Engineering Fields - Instrumentation Engineering - New Member Engineering Fields - Control Engineering - Who am I?

Join Date: Oct 2006
Location: Northern Mindanao, Philippines
Posts: 2147
Good Answers: 53
#2

Re: Temperature Controller Calibration

07/23/2009 8:07 AM

What do you mean by "different heater"?

Are you using a heater with a different rating (e.g. 120W vs 100W)?

Are you using a different brand but with the same rating?

Are you using heaters with different diameters or lengths?

The answers to these questions will determine what the correct answer will be. Please provide more information.

If you're using the heaters with the same wattage, you should be fine if the heater fits into the heating bar as well as the original. If it is a loose fit, you'll have problems getting the same performance.

If you didn't change the temperature sensor, I don't see how changing the heater will affect the calibration. The new heater may be slower or faster, or it be more powerful or less powerful than the original, but that will only affect the performance, not the reading.

regards,

Vulcan

__________________
Miscommunication: when what people heard you say differs from what you said. Make yourself understood.
Register to Reply
Guru
Hobbies - DIY Welding - pipewelder

Join Date: Apr 2007
Location: North Georgia, USA
Posts: 671
Good Answers: 33
#3

Re: Temperature Controller Calibration

07/24/2009 2:56 PM

Are you using the same type thermocouple as you did with the other controller? Temp. controllers are usually set for a certain type thermocouple (j, k, s, r and so on) I have had problems before with a controller being set for a J type and I would be trying hook it to a K type thermocouple or visa versa. Most PID controllers are able to be set to several different type thermocouples in the programing menu. This is just an idea but I think it is worth checking before troubleshooting further and usually it is very easy to check. I have several Watlow brand controllers in use and they are very simple to check and/or change the thermocouple type and they will not be accurate if it is not set correctly.

__________________
pipewelder
Register to Reply
Active Contributor

Join Date: Jul 2009
Location: Cavite, Philippines
Posts: 10
#4

Re: Temperature Controller Calibration

07/31/2009 1:57 AM

Yes, very necessary. By calibration you are comparing your instrument reading or measurement to a standard of known acurracy (calibrated also to a national/international standard traceable to national metrology laboratory in your place)

Now a days, its very simple to calibrate controllers, they are users friendly.

You said that you are getting different reading because you used different heater.

Using different heater higher or lower rating, the cycle time of on and off is affected, you may need to to adjust its P, I, D parameters to tune again to its response to load deviation, that's why you are getting different reading.

If your cotroller has auto tune function try to swicth it on, if still you not getting good response, Try asking a help with your machine supplier.