400V Sub-DB Busbar Insulation Spacing

07/22/2009 9:28 PM

We need to order a new sub-DB of 400V. Not sure what is the required space insulation between busbar phases. Is there any international standard for this requirement? What about those insulated busbar? The required spacing is much lower?

Thanks.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#1

Re: 400V sub-DB busbar insulation spacing

07/22/2009 10:10 PM

Is there any international standard for this requirement?

Yes there are. If you are ordering a complete switchboard from a switchboard manufacturer or supplier then it should be built to the standards applicable to your country. If you are wanting to buy sub assemblies (like bus work) and build your own then you will need to provide us some more information as the applicable standards vary from country to country.

__________________
jack of all trades
Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#2

Re: 400V sub-DB busbar insulation spacing

07/22/2009 11:17 PM

Whether you use Insulated Busbar or Bare Busbar, you need to have enough spacing between each busbar with the minimum distance of 60 mm to 75mm.

60mm to 75mm is not the standard requirement distance for the safety of the busbar but it is for your own maintenance works where you need to tighten these busbar connection (busbar to busbar) in later stage or you need to tighten the busbar holder inside your Sub Board.(if found to be loosen)

Where will be a time where you need to tighten the blot and nut at the incoming compartment to your breakers or your cables that connected to the busbar.

If you have too small distance between these busbar, later stage you will find difficulties to do your maintenance works.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Anonymous Poster
#3

Re: 400V sub-DB busbar insulation spacing

07/22/2009 11:29 PM

Hi

there are always some standard requirement for this also, as per standard minimum clearance depends on the material group and pollution degree of the insulating material which is further derived from Comprative Tracking Index (CTI).

in addition to this, space required to do some work on bus bar are also to be considered,

so its vary from country to country and manufacturer to manufacturer,

Thanks & Regards

Divyesh patel

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: 400V sub-DB busbar insulation spacing

07/23/2009 3:28 AM

CE-marked equipment is type-tested as suitable for application throughout the European Economic Community.

Don't reinvent the wheel. Go shopping instead!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Reply to Forum Thread 4 comments
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); jack of all trades (1); PWSlack (1); Simon Wan (1)

Previous in Forum: Polarization Index   Next in Forum: Maximum Demand Loads

Advertisement