Dear all can any one tell me the what will be the effect on delta P if nos of plate incraeses in a plate type heat exchanger
is there any formula to calculate the exact pressure drop
thx in advance
Re: Pressure drop in plate type heat exchanger
07/23/2009 3:45 AM
If the flowrate through the unit stays the same, the number of pathways through the exchange increases when adding plates, so the pressure drop reduces. However, there is a pay-off. With lower pressure drop the velocity between plates reduces, which reduces the turbulence, which reduces the heat exchange per plate.
The best advice would be to discuss the proposal with the manufacturer, who will have experience of applying the products across a wide range of applications and will be in the best position to advise.
Good Answers: 16
07/25/2009 7:49 AM
I would think the pressure drop increases rather than reduces when adding plates huh?
By the way PWSlack, what is that thing pictured in your aviator anyway???
Good Answers: 103
07/25/2009 8:03 AM
PWS is right.
More plate means also the size of the HE is increasing (you do not insert plates in between rather at the end. So more crossection for fluid.