Just compare the CT sizes with the ones that have the name plate on it. Each CT have different sizes for each application.
__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Try a burden test, find the point at which each coil fails to perform up to standard, and compare your results to a similar transformer that has a nameplate.
Are the terminals also not marked? Perhaps the transformer is in service and you don't want to get close enough to visually inspect the nameplate and terminals?
Regards, CJM
__________________
I do not 'know it all', but i will admit that I would like to. CJM
Thank you,actually I was also thinking a VA characteristick test to find the linearity; metering CT expected to have more linear than the protection but how I identify the PS core.
Number one on your list is, "Very carefully". CTs have a habit of generating very high voltage when cut off from source. The voltage induced into the high voltage side, with current, can produce and output voltage of up to 1 MV (million) on the low voltage side. I would send the Ct's back or send them to someone who has experience with such an item.
__________________
Could be worse, it could be me. :)