Arranging Alarms for Tripping Motors

07/29/2009 9:22 PM

Hi, Friends

I need a suggestion for installation of an alarm system for the tripping of motors for agitator & circulation pumps to avoid loss of production. Appreciate if someone can guide indicating the basic requirement for the procurement of electrical items as well as circuit diagram.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#1

Re: Alarm Arrangement for Tripping of Motors

07/29/2009 11:42 PM

Does your control panel have a tripping lamp indicator and what is the lamp voltage. If you control panel have these motor tripping lamp indicator then it will be a easy circuit to design and the component used will be less

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2

Re: Alarm Arrangement for Tripping of Motors

07/30/2009 12:15 AM

Waiting for a light to come on AFTER the motor overload has already tripped is like closing the barn door after the horses have escaped.

I think a better approach may be to upgrade your motor overload relays to one of the new type that have some programmable functions. That way you can set them up at some level below the trip setting to WARN you of an impending trip so that you can do something about it to avoid an unscheduled shutdown. For instance Siemens makes a product called a Simocode Relay that would be capable of doing this. You can also tie it in to a network and a PLC to take actions appropriate to the purpose of avoiding the shutdown conditions, for example slowing down a feed rate or something.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply Good Answer (Score 2)
Guru

Join Date: Dec 2007
Location: Cypress Calif
Posts: 741
Good Answers: 23
#7
In reply to #2

Re: Alarm Arrangement for Tripping of Motors

07/31/2009 5:07 AM

Hello Jraef:

You're a wealth of information about these newfangled gadgets. I would've merely used a contractor with an auxiliary contact to set off an alarm. Definitely better to find the problem before it occurs.

__________________
"The reasonable man adapts himself to the world; the unreasonable one persists in trying to adapt the world to himself. Therefore all progress depends on the unreasonable man" George Shaw
Reply
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#3

Re: Alarm Arrangement for Tripping of Motors

07/30/2009 3:09 AM

As simple as this will work.

Reply Score 1 for Good Answer
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2006
Location: Rochester, NY
Posts: 867
Good Answers: 11
#9
In reply to #3

Re: Alarm Arrangement for Tripping of Motors

07/31/2009 8:29 AM

Everybody else is telling the guy how he should be doing it differently. You are the only person who answered the question. It's bemusing, isn't it? GA for cutting the chase.

__________________
Eric
Reply Off Topic (Score 5)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#11
In reply to #3

Re: Alarm Arrangement for Tripping of Motors

07/31/2009 7:30 PM

I don't see how that is going to solve anything. From what I see there, it is for a small 1 phase motor and whenever the motor draws current, the buzzer will go off. What value does that offer other than being very annoying?

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#12
In reply to #11

Re: Alarm Arrangement for Tripping of Motors

07/31/2009 10:51 PM

JRaef with due respect,

I am not here to defend my GA, Neither I do say that none of other answer offer any value, But at the same time we should look in to precision of answer with ref to what OP is asking for.

We don't know how frequent is tripping of motor, may be its once in a 15days.If that is the I case I don't see any reason to replace motor anyway.

You wrote,

it is for a small 1 phase motor and whenever the motor draws current, the buzzer will go off. What value does that offer other than being very annoying?

No, it can be used in three phase motor of any size, Three phase motor don't require a three phase alarm.And its not whenever motor draw current buzzer will go off, Infarct its whenever motor stop drawing current buzzer will go on, and then its going to annoy, Isn't that what OP want?

Regards.

Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: Alarm Arrangement for Tripping of Motors

07/30/2009 3:17 AM

Once a trip has operated and an alarm is active, the process is in peril.

The question needs alternative consideration.

  • What things need to be done to the equipment to minimise the risk of a trip operating and an alarm being raised so that the process continues without peril?

This is a subject for discussion at a HazOp study, in the simultaneous presence of process people, operations people, instrumentation people, mechanical people, and can only be done locally.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Score 1 for Good Answer
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#5

Re: Alarm Arrangement for Tripping of Motors

07/30/2009 9:43 AM

The correct method is using thermistors for LV motors and for HT Its different.I presume u are refering to a low voltage motor.Motor manufactures can supply motors with thermistors .Now a motor with class B insulationr made for an ambient temp of 40Deg C (In India Its 50)the permitted temp rise is 80 Deg C Over 40Deg C Amb making the total to 120Deg C.Class B max temp allowed is 130DegC with 10Deg C reserved for hot spots.Normally 2 sets of thermistors 2 per phse are embedded in the windings one one for 120DegC and One for110DegC.It comes with a small relay which can be mounted on the panel.At 110Deg u will get the alarm and can take action to reduce the temp by redusing load If alarm is over looked at 120DegC it will trip the motor and prevent burn out.there are 2 types of thermistors possitive temp coefficient and negative temp. coeff.Each Phase we need 2 nos.It also comes with a simple realy having 1no+1NC Contact.If your existing motor does not have it you can procure it with the realy and embed in the over hangs of the stator winding and connect the realy suitably.

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply
Commentator

Join Date: May 2007
Location: Cebu, Philippines
Posts: 94
Good Answers: 2
#6

Re: Arranging Alarms for Tripping Motors

07/31/2009 1:18 AM

If you have the system designed properly,( correctly sized motors, correct impellers, etc.) the tripping of the motors and circulation pumps should not occur that often. Tripping can only happen unless there is a power fluctuation or a voltage drop. An alarm system will not be of much help because the motors have already stopped and the operator will still have to restart the system. But before you resume to operate, it is still a proper procedure to determine what has caused the tripping.

__________________
rusale
Reply
Participant

Join Date: Jul 2009
Posts: 2
#8

Re: Arranging Alarms for Tripping Motors

07/31/2009 5:46 AM

May be you can use pressure alarm contact to indicate pre-tripping alarm for the motors. Or if you can choose Variable Voltage Variable Frequency Drives (VVVF) for smoother control as well as power saving

Reply Off Topic (Score 5)
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#10
In reply to #8

Re: Arranging Alarms for Tripping Motors

07/31/2009 8:39 AM

Thermistor is the cheapest and best when u need alarm or trip or both.

__________________
To avoid crticism do nothing,say nothing,be nothing
Reply Off Topic (Score 5)
Guru

Join Date: Dec 2007
Location: Cypress Calif
Posts: 741
Good Answers: 23
#13

Re: Arranging Alarms for Tripping Motors

08/01/2009 4:56 AM

Hello Guest:

Several workable suggestions have been made. If you could please provide a little bit more information such as are these three phase motors or single phase and what type of budget are you trying and stay in. It might help to decide the best solution for you.

A kiss principle solution if they are three-phase and controlled by a mags would be to install a auxiliary contact on the Mag or it might already be present and use that contact to trip your alarm circuit.

This is a very simple circuit and requires no electronics. You merely route the power for your alarm through a dry contact.

In the alternative there are combination current sensors/contacts available. A little more expensive but will work with single phase or three-phase and very simple to install. The link below will take you to an example of one.

http://www.grainger.com/Grainger/items/6C057

This has several advantages over some of the other solutions. It can be programmed to trip below your anticipated overload current and thus provides you advance warning.

One of the workable solutions offered would have you build a custom circuit, in my opinion it's always better if possible to go with off-the-shelf products, you may understand the custom circuit however if you're not available the next repair tech may not.

These current sensors are extremely simple to install, merely route one of the current carrying conductor's that is going to your motor through the loop. Provide the sensor power supply (they are available in various supply voltages) and connect your alarm through the dry contacts provided on the sensor.

Since there are many other ways to do this additional information may provide you with a better solution, any of us can provide you with a wiring diagram.

__________________
"The reasonable man adapts himself to the world; the unreasonable one persists in trying to adapt the world to himself. Therefore all progress depends on the unreasonable man" George Shaw
Reply Score 1 for Good Answer
Reply to Forum Thread 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

ca1ic0cat (1); JRaef (2); nesubra (2); PWSlack (1); rakesh_semwal (2); rupertal (1); Simon Wan (1); Srinivasu V (1); YWROADRUNNER (2)

Previous in Forum: Rotor Insulation IEEE 43   Next in Forum: MCD framing
You might be interested in: DC Motors, Stepper Motors, AC Motors

Advertisement