Connecting Power Flex 4 VFD to SCL 5/03 PLC

08/07/2009 6:33 AM

can i connect powerflex 4 vfd to slc 5/03 plc if ihave net aic converter .can i send directly ladder logic like start ,stop and analog 0-10 volt signal to power flex 4 with rs485 port .

plz tell me how this is poosible and which block will be used in ladder logic to send all signals.

i need full details for this option .

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: power flex 4 vfd

08/07/2009 6:50 AM

Ladder logic isn't "sent" to the vfd, or anything else for that matter. It merely determines when certain PLC outputs are on depending on the PLC inputs and the recipe inside it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Active Contributor

Join Date: Jul 2009
Location: india
Posts: 12
#2
In reply to #1

Re: power flex 4 vfd

08/07/2009 6:57 AM

if ladder logic can not sent to vfd then what is option to send all start stop and freq comand mode signal to vfd by rs485 port . if slc 5/03 and net AIC adopter and vfd and rj 45 connecter .

any massege comand is given by slc 5/03 allen bradely plc .

Register to Reply
Power-User

Join Date: Aug 2007
Location: San Francisco Bay Area
Posts: 266
Good Answers: 21
#3

Re: Connecting Power Flex 4 VFD to SCL 5/03 PLC

08/08/2009 12:28 AM

You can talk to the Flex from the 5/03. It's not that difficult. Refer to appendix c in the flex4 book for the 06 registers and bits to write.

If you have a long run between the PLC and the drive (stay within 4000ft) or you have multiple drives to control then use the df1 capability.

Don't try to be fancy if you just have a simple drive to run. You're usually much better off just using an analog output card for your 0-10v speed ref and a few outputs. Real simple logic there.

Here's an example that should help though:

http://forums.mrplc.com/index.php?s=431d5fef782cb4adfcc5c4430ddda99e&showtopic=17165

__________________
Speed doesn't kill. Sudden stops, brick walls, and old ladies in Buicks do.
Register to Reply