APFCs for DG Sets

08/10/2009 3:41 AM

At our site, we have 2 nos. of 500 KVA DG sets. The factory was being operated on DG sets till recently. APFC panels were also installed long back but were not put into service. Couple of days back we have received EB (State Electricity Board) power. Now, the APFCs (Automatic Power Factor Controllers) are commissioned and pressed into service.

My question is why APFC are not used with DG sets?

Regards,

PG

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster
#1

Re: APFC (Automatic power factor controller) for DG sets

08/10/2009 5:04 AM

Some gensets are equipped with their own built in PFCs, hence no need to controll PF

Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: APFC (Automatic power factor controller) for DG sets

08/10/2009 6:16 AM

It is the load characteristics that determine the need for PFC and the tariff that deterrmines the economics of using them. Ordinarily, PFC is placed at the end of a transmission line to improve power factor within the line and to reduce transmission losses.

If the EB has imposed a penalty on the tariff for low power factor on the new connection then the use of PFC now will be an economic one based on the avoidance of penalty charges to the EB, and this explains the commencement of use.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#3

Re: APFCs for DG Sets

08/10/2009 3:16 PM

dear,

good logic !

But,

As you are convinced that State electricity Board give you rebate if the average power during the billing month is maintained at 1.0 ( > 0.96 ) so, definitely, you shall set the APFC instrument for power factor 0.98 or 1.0 .

But, as you shpould be aware that DG sets do not work properly at leading power factor . So, if APFC was ON with DG sets running, with some manufacturer's APFC instruments, as CT current sensed is zero, ( CTs being placed in SB line ), all the capacitors will be switched ON. dg shall operate at leading pf, damaging the shaft or engine.

But now a days, microprocessor based digital APFCs are available that do not switch on all the capacitors , in that case, you could have been started the APFC even priior to SB supply is received. Only, all the capacitors would be off as the CT sensing is at zero current. As CTs are placed in SB line.

Further, I have seen APFC relay with 2 Incomer CTs. You can set different values of PF for each CT incomer.

Incomer 1 - CT placed in SB line - PF set = 1.0

Incomer 2 - CT placed in DG line - PF set = 0.8 lag.

__________________
Exploring the Science of Electricity
Reply