08/15/2009 2:55 AM

why we give transformer rating in VA.why not in kva or kw.

regards

Rizwan.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#1

Re: Transformer Ratings

08/15/2009 12:11 PM

Because the load on a transformer seldom has a power facator of one.

Reply
Anonymous Poster
#2

Re: Transformer Ratings

08/16/2009 2:17 AM

why we give transformer rating in VA.why not in kva or kw.

We do give it in KVA and MVA too

Why not in - W, KW, MW, HP, ft-lbs, cph, BTU/H etc search the previous threads.

Reply
Anonymous Poster
#3
In reply to #2

Re: Transformer Ratings

08/16/2009 9:17 AM

Transformer is a very effecient elect. machine designed with a unity power factor=1.

In this reason therefore the Kw=Kva Note: always refer back to power triangle theory, therefore you can visualize the relations of Kva, Kw and Kvar.