08/16/2009 5:03 AM
Q. What is the method to find out the exact pickup current settings of a "time overcurrent relay" and the tripping curve used/selected in an old electronic relay.
Re: Time Over Current Protection Relay
08/16/2009 10:53 AM
dear,
so many parameters to check....
characteristic curve - wether 1.3 sec, 3 sec.
fault level of your system
ct ratios
hint - normally, 10 * Ir of fault current of meter = trip time of 1.3 / 3 sec depends upon the characteristic .
accordingly, you may set your relay with desired trip time setting.
Exploring the Science of Electricity
08/17/2009 3:47 AM
How about measuring it?
Never trade luck for skill.
United States - Member - Member Engineering Fields - Power Engineering - New Member
08/17/2009 8:53 AM
Sounds like the first thing you want to find is a qualified relay technician, or equivalent person. The relay tech would be equipped with a test set that directly interrogates the relay function. A common test procedure would be to test and calibrate the Long Time (LT) pickup and two points on the delay curve (Lever or Timer Dial). Then test & calibrate the Instantaneous Action (IA). The relay tech should have the curve from the original instructions booklet, which is usually noted on the manufacturer's name plate on the relay.
Good Luck
08/17/2009 11:46 PM
Dear Gentlemen,
We have an assignment to replace some very old model electronic Time overcurrent relays with the new model digital relays. The settings for the old relays are not available. We want to find out the existing settings so we can configure the new relays accordingly. Because if the new relays are not configured properly these may effect the up stream or down stream protection system.
We have the latest secondary injection test set alongwith a qualified technician but we are confused to get the exact existing settings. Thats why I put this question here that may be some one faced the similar problem and might help us.
Q1. How we can find out its exact pickup current (not tripping current)?
Q2. Curve used alongwith its multiplier settings. I mean how we can compare its tripping current and time with the standard Curves (IEC, ANSI or IAC) etc. so we can assume that this specific curve and multiplier was used when this relay was configured.
If we have this data available then it is easy for us to configure the new digital relay which will replace this existing old model relay.
Thanks and best regards
Manzoor H.
08/17/2009 11:45 PM
Dear Gentlemen,
Manzoor H.