Anonymous Poster

Motor Overloads and Service Factors

08/16/2009 10:17 AM

what r the formulea for setting overload for a motor having service factor of 1 and 1.15

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#1

Re: how ll i sett overload

08/16/2009 10:33 AM

what do you mean by service factor ?

Normally, over load relay is current operated. Motor should not draw the current more then its rated continuous current. But, we normally set the relay at the actual maximum load current, which may be less then the motor rated current. This protects indirectly the mechanical equipment / malfunction in the process also.

__________________
Exploring the Science of Electricity
Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2
In reply to #1

Re: how ll i sett overload

08/16/2009 10:53 AM

Service factor is the amount of overload the motor is designed to tolerate. A service factor of 1.15 means that the motor can be safely run at 1.15 times the rated amps.

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3
In reply to #2

Re: how ll i sett overload

08/16/2009 1:31 PM

Temporarily

For those not in the US or Canada, Service Factor is a NEMA motor terinology related to a percentage of short duration additional load that can be applied to a motor. Although there is no "official" definition of "short duration", it is understood that service factor is meant to be left alone so that the motor can withstand temporary low voltage conditions or unusually heavy loading. That said, many OEMs ignore this and design motors into their equipment such that the SF is used continuously, and if challenged will point out that the NEMA definition does not define a time limit. Brinksmanship is generally considered bad engineering practice but is not unheard of.

So with that in mnd, the BEST practice is to set OLs to the motor FLA and no more. IF YOU MUST USE THE SF, then set the OL relay to the absolute lowest amount you intend on using. For example even say your motor is labeled as 1.15SF, if you can do the job with 1.10, then set the OLR to 110% of FLA. For every 10 deg. C rise in motor temperature over t's rated temperature, you cut the life of the insulation in half. So anything that raises the core temperature is lowering the motor life. Running into the SF is acknwledged to be purposefully raising the temperature, thus removing any "fudge factor" you may have had.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Participant

Join Date: Aug 2009
Posts: 4
#7
In reply to #3

Re: how ll i sett overload

09/07/2009 1:10 PM

Actually i want to make myself understand by provide you an example

Suppose a motor is having service factor of 1 and the full load amps are 20 what ll b my setting on the overlaod ll it be 20 Amps, 18ampsor 22amps.And if the same motor is having service factor of 1.15 what ll be my setting on overload ll it be 20 Amps, or 22 Amps\

Pls guide me accordingly

thanks

Reply
Anonymous Poster
#4

Re: Motor Overloads and Service Factors

08/16/2009 7:00 PM

For you, I recommend setting the overload to it's maximum for all the motors in your facility. Please also remove all the safey guards from the prime movers as they will interfere with proper operational maintenance. If you have dangerous chemicals, store them in a heavily populated area such as a cafeteria or break room.

While you're at it, replace all the fuses with peices of conduit or dowel rods wrapped in aluminum foil.

Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#5
In reply to #4

Re: Motor Overloads and Service Factors

08/17/2009 4:17 AM

Dowel rods, if made from wood, make terrible fuses.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Reply
Anonymous Poster
#6

Re: Motor Overloads and Service Factors

08/17/2009 7:57 AM

I recommend to read the NEC Hand book Article 430 may be it can help you as a reference guide.

Reply