Transformers and Secondary Voltage

08/19/2009 7:20 PM

For 3750KVA rated transformer, how would u know the secondary voltages with primary being 44000V

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#1

Re: secondary voltage of transformer

08/19/2009 7:31 PM

Find the specs plate thats typically attached to it. Or find out where it was used and what voltage they were getting from it. Or contact the manufacturer.

If possible count the primary and secondary coil turns and factor out the ratio.

Reply
Guru

Join Date: Sep 2007
Location: Defreestville, NY
Posts: 1072
Good Answers: 87
#2

Re: secondary voltage of transformer

08/19/2009 8:27 PM

Read the label?

__________________
Charlie don't surf.
Reply
Guru

Join Date: Apr 2007
Posts: 577
Good Answers: 10
#3

Re: secondary voltage of transformer

08/19/2009 9:07 PM

All transformer has a specification name plate, stated the primary input voltage, secondary output voltage, KVA, frequency and e.t.c. That, is the only identification tag available to identify the specification of the transformer.

It is not possible to use the transformer capacity KVA to determine the secondary voltage. Maybe you need to ask around and see if any people using this type of transformer with the same capacity and the same primary voltage. But then again, even they do have it as the same transformer as your unit, your chances of accuracy of guessing the secondary voltage still remain at 50-50 % correct.

The best way is to ask the manufacture to test it.

__________________
Management is just like a bunch of Monkey sitting on a tall tree. Some climb to the highest branch and some at the lowest branch. The highest Monkey look down and see a lot of happy faces but the lower Monkey looks up and see nothing but all the....
Reply
Active Contributor

Join Date: Aug 2008
Posts: 19
#4

Re: secondary voltage of transformer

08/20/2009 1:18 AM

Very easy, just use transformer turn ration test (TTR) equipment which will give you the exact turns ratio of transformer windings "Secondary & Primary" and then simply calculate the secondary voltage.

Good Luck

Reply
Commentator

Join Date: May 2009
Location: Centurion, South Africa
Posts: 87
Good Answers: 5
#5

Re: secondary voltage of transformer

08/20/2009 1:23 AM

Do you know if this is a step down transformer? If so you may put a 400v three phase supply on the primary winding and measure the output voltage on the secondary. From the input and output voltages you will be able to calculate the ratio.

__________________
R T F M .......
Reply
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#6
In reply to #5

Re: secondary voltage of transformer

08/20/2009 6:53 PM

Do the steps below:

1. Look into the transformer bushing and clearly identify the HT and LT side. The HT bushing is larger than the LT bushing.

2. Apply 3 phase low voltage (say 440V L-L) to HT side. Keep the LT side Open

3. Precisely measure the LT side Line to Line voltage (say 4 V)

4. As you said your primary is 44000 V, then your secondary voltage will be (44000 x 4) / 440 = 400 V

Precaution:

  1. It is very important to identify the HT and LT side first and then proceed, otherwise DON'T PROCEED to STEP 2.
  2. Make sure you apply voltage in HT side, NOT in LT side.

-MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Reply Good Answer (Score 2)
Commentator

Join Date: Sep 2009
Posts: 59
Good Answers: 3
#7
In reply to #6

Re: secondary voltage of transformer

09/16/2009 12:51 AM

Just to add a little.The HV bushing is taller in height with smaller conductor.The LV bushing is much shorter but bigger in diameter,with very thick copper terminal.For DYn transformer,3 bushing on primary and 4 bushings on secondary side. ( don't buy transformer from scrap yards )

Regards,

Khor

Reply
Reply to Forum Thread 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".
Copy to Clipboard

Users who posted comments:

Aldego (1); Khor (1); manzoor14 (1); msamad (1); Simon Wan (1); stevem (1); tcmtech (1)

Previous in Forum: Diesel Generator Service in Western Canada   Next in Forum: Delta Star Transformer

Advertisement