Delta Star Transformer

08/20/2009 1:49 AM

what would happen to secondary voltages of the delta star transformer if one of the phases on the primary side goes off (i.e. supply to that phase gets disconnected?)

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: delta star trnasformer

08/20/2009 3:16 AM

The secondary output will drop too. Possibly some of the circuit protective devices will operate.

It is more likely that two phases will go, and not one, on the primary side. If that happens, the secondary output will drop to zero.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2
In reply to #1

Re: delta star trnasformer

08/20/2009 9:49 PM

Please see the following thread, it may help.

http://cr4.globalspec.com/thread/40007

-MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru

Join Date: Sep 2008
Posts: 706
Good Answers: 32
#3

Re: Delta Star Transformer

08/21/2009 10:08 AM

I had a Delta wound transformer supporting our 220-3 phase secondary system and the utility transformer blew a link up on the pole. Our 3 phase machinery slowed down noticeably, some popped off and we quickly shut all the 220v-3 phase down before the rest could overload. We lost a 220 single phase on the boiler circulator because no one remembered that it was on 220.

On a Delta wound transformer each leg only carries 57.7% on the current on each leg. It tends to balance out the loads on each leg. However, when you lose a phase you now have an "open Delta" and the system can't support the full load.

Another time we lost one of the three 100A fuses at the disconnect protecting a Delta wound Transformer with the same resulting slowdown of machinery. Fortunately we had learned our lesson from the first incident and saved everything that time.

__________________
Spinco
Register to Reply