50-Hz Ballast in 60-Hz System

08/20/2009 6:18 AM

Dear Sir,

We are having fluorescent lamps with Electronic as well as Electromagnetic Ballasts,which are rated for 50 Hz operation, but our supply is 60 Hz and voltage is matching with rated voltage. Kindly let me know whether there is any effect on ballast or lamp due to this mismatch of frequency.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Aug 2007
Location: Toronto
Posts: 239
Good Answers: 9
#1

Re: 50 Hz Ballast in 60Hz System

08/20/2009 9:46 AM

Have you asked the manufacturer?

Register to Reply
Guru

Join Date: Jun 2009
Location: South of Minot North Dakota
Posts: 8376
Good Answers: 775
#2

Re: 50 Hz Ballast in 60Hz System

08/20/2009 12:30 PM

Typically most ballasts will take the higher frequency with out any problems at all But the power factor or current limiting capacitor may need to be replaced with a smaller value. If so one about 5/6 of the original capacitance value is typically about right or at least close enough.

Many ballasts are 50 -60 Hz rated and require no changes. Without knowing for sure contacting the manufacturer is typicaly the smartest way to go.

Register to Reply
Anonymous Poster
#3

Re: 50-Hz Ballast in 60-Hz System

08/21/2009 1:50 AM

A 60Hz 220volt rated FTL electromagnetic ballast will make lamp perform same as 50Hz 240 volt electromagnetic ballast with only diffrence being ballast losses(and vise versa)However PF improvement capacitor value shall be adjusted to take care of losses change and frequency change.

Register to Reply
Power-User

Join Date: Jun 2008
Location: Olive Branch, Ms. USA
Posts: 124
#4

Re: 50-Hz Ballast in 60-Hz System

08/22/2009 1:07 PM

The problem that you will likely face is the same one for all electrical components dsigned for 50Hz operating on 60Hz. That is a shortened life expectancy.

__________________
Tell 'em what they need to hear; not what they want to hear!
Register to Reply