Synchronous Generator Keeps Stopping

08/20/2009 12:06 PM

Dear folks,

I am a newbie here, so please don't mind if i am not that descriptive of the subject.

Well, we have a 15 MVA synchronous (hydro) generator with 14 poles,horizontal shaft arangement, rated speed of 428.6 rpm and moment of inertia of 12,000 kgm2. Recently, the machine tripped on some temperature fault and the machine came to a complete standstill within less than 3 minutes against a normal time of 35-40 minutes. We don't have any type of braking mechanism put in place. We were completely shocked by its unusual behaviour and inspected the runner, the NDE and DE bearings, air gap, IR of the stator windings, XLPE cable, etc. Everything was normal but we were skeptic to run it. However, we did run the machine and everything was just normal.I just want to know whether anybody has ever experienced such incidence or have knowledge about what could be the reason.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
Australia - Member - Igor...pull the switch!!!

Join Date: Apr 2009
Location: Australia, sunny North Queensland
Posts: 380
Good Answers: 12
#1

Re: Synchronous Generator Keeps Stopping

08/20/2009 9:44 PM

My level of education re generators is limited to DIY home brew types. I was going to point the finger at the stator, but you checked that out.

The generator you wish to trouble shoot, you describe it as braking and tripping a temperature fault? Assuming that is the case (and assuming you are not using permanent magnets-if you were, got any spare ones, lol), I would examine the frequency and voltage source fed to the synchronous generator used for the sole purpose of excitation of the salient rotor. I assume here, your field winding is on the rotor and the armature winding is on the stator.

It is possible (my uneducated answer) a frequency or voltage shift may have occured at your source fed to your generator, causing the heat and braking effect you describe.

__________________
CraziestOzzy
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#2

Re: Synchronous Generator Keeps Stopping

08/21/2009 7:50 AM

If it was still electrically "loaded" in some way, this would work as a brake......even a (partial) short on the output would have the same effect.

A short would maybe explain the over temp as well......

Did you check for earth/ground faults?

Just my 2 (Euro) Cents worth!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Apr 2007
Posts: 178
Good Answers: 3
#3

Re: Synchronous Generator Keeps Stopping

08/21/2009 8:10 AM

Sounds like you have checked all the obvious, In order to stop that much rotational energy in that short a period, there must have been a lot of energy dissipated somewhere, either electrical or hydraulic. (no brakes or damage just about eliminates the mechanical.)

The temperature fault might be a clue. I assume it's from a number of imbedded temperature sensors on a common alarm/trip. If there was field excitation present during the coast down and a possible shorted turn condition in the stator windings, it could cause a hot spot and the shorted turns would absorb energy and create a braking action,

Shorts of this type do not generally heal unless the short point contact is still present and the shorted turn has burned open during the coast down. I'm afraid your problem may come back to haunt you again, (just some thoughts) .

Your horizontal shaft configuration and machine size indicates to me that this may be a low head "Peltton" runner, is that true.